Greetings.
I tested an rfc and recorded the following results:
r1 = 0.62
rN = 0.89
r2 = 1.45
The difference in r1 and rN indicate loose connections so I checked all the sockets (bar one) on the ring which revealed two loose connections.
The rfc now tests as follows:
r1 = 0.58
rN = 0.59
r2 = 1.45
The measurements indicate a 80 metre circuit of 2.5mm^2 csa.
I've checked every socket in the dwelling except one which feeds a waterbed and is inaccessible. So I told the customer that I have some homework to do before I can issue certification.
BUT, I hadn't realised that it could be 2.5/1 t&e in which case the measurement of 1.45 (remaining constant) is correct.
I don't have a micrometer to measure the cpc so how do I confirm the cable conductor's csa? ... and if it's 1mm^2 cpc is that okay?

The wiring is about 25 - 30 years old.
 
what you could try is connect L to E on one side of the ring and leave the other open at the board, check the R1 R2 readings at the sockets nearest then move further along until you notice any major jump , if its a gradual increase on all then o/k ,
 
what you could try is connect L to E on one side of the ring and leave the other open at the board, check the R1 R2 readings at the sockets nearest then move further along until you notice any major jump , if its a gradual increase on all then o/k ,
to make this quicker, wire a plug with a bit of flex from it going to connector strip.

this makes it quick to a quick check without removing fronts (very useful if there if there is a dead short somewhere)

or if you have a multimeter etc with non gs38 leads just shove them in the socket
 
Thanks, R G,
The route the cable takes is not obvious but I sort of did what you're suggesting with expected results.
If the cpc is 1mm^2 is it acceptable (i.e. compliant with BS767)?
 
I would compare a bit of new cable with the old , for the earth wire size , if you have test leads to a plug then you won't need to remove the socket fronts ...

If you have done this then as shanky says if Zs is good at end of circuit then its o/k
 
I would compare a bit of new cable with the old , for the earth wire size , if you have test leads to a socket then you won't need to remove the socket fronts ...

Thanks again R G,
I started to doubt myself and stopped thinking clearly.

Is it satisfactory to have a 1mm cpc on a rfc protected by a 32A type b breaker?
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

zap

-
Joined
Location
Southboune, Dorset

Thread Information

Title
Identifying csa of t&e
Prefix
Forum
UK Electrical Forum
Start date
Last reply date
Replies
24
Unsolved
--

Advert

Thread statistics

Created
zap,
Last reply from
zap,
Replies
24
Views
3,029

Advert

Back
Top