zap

-
Joined
Feb 14, 2011
Messages
214
Reaction score
65
Location
Southboune, Dorset
Greetings.
I tested an rfc and recorded the following results:
r1 = 0.62
rN = 0.89
r2 = 1.45
The difference in r1 and rN indicate loose connections so I checked all the sockets (bar one) on the ring which revealed two loose connections.
The rfc now tests as follows:
r1 = 0.58
rN = 0.59
r2 = 1.45
The measurements indicate a 80 metre circuit of 2.5mm^2 csa.
I've checked every socket in the dwelling except one which feeds a waterbed and is inaccessible. So I told the customer that I have some homework to do before I can issue certification.
BUT, I hadn't realised that it could be 2.5/1 t&e in which case the measurement of 1.45 (remaining constant) is correct.
I don't have a micrometer to measure the cpc so how do I confirm the cable conductor's csa? ... and if it's 1mm^2 cpc is that okay?

The wiring is about 25 - 30 years old.
 
1.omm cpc is acceptable provided that you calculate the min. size of cpc from the pefc, using the adiabatic equation and the trip time of the ocpd. ( usually 0.1 sec. with a k value of 115).
 
1.omm cpc is acceptable provided that you calculate the min. size of cpc from the pefc, using the adiabatic equation and the trip time of the ocpd. ( usually 0.1 sec. with a k value of 115).

This is too good an opportunity to check my understanding of the adiabatic equation.

Type B breaker

I = 5 x 32A = 160A
t = 0.1
k = 115
S = minimum csa

S = SQR(I² x t) ÷ k

50.6 ÷ 115 = 0.44 mm²

Therefore 1mm² is good to go.
 
Last edited:
Not quite.

You need to calculate the ACTUAL disconnection time with the ACTUAL fault current at that point. Typically a BS EN 60898 circuit breaker has an instantaneous operating time quoted as 0.1 seconds, however if you consult the manufacturer's data then there may be a definite minimum operating time of around 0.01 seconds at your value of prospective fault current at the extremity of the circuit. This could help achieve a smaller cpc csa.

Then so long as the result, i.e. S, is no greater than the cpc cross-sectional area that you have then it is adequate. This is an iterative calculation, so when designing you would have to recalculate as you increase the cpc csa as this will affect the Zs and prospective earth fault current, which will subsequently affect the size of cpc given as the minimum (i.e. it will increase - so you need to ensure that your new csa is adequate after calculation).
 
Thanks again R G,
I started to doubt myself and stopped thinking clearly.

Is it satisfactory to have a 1mm cpc on a rfc protected by a 32A type b breaker?

Sometimes it is and other times it isn't. Just calculate it using the adiabatic equation the same as you do for the cpc of all the circuits you install.
 
This is too good an opportunity to check my understanding of the adiabatic equation.

Type B breaker

I = 5 x 32A = 160A
t = 0.1
k = 115
S = minimum csa

S = SQR(I² x t) ÷ k

50.6 ÷ 115 = 0.44 mm²

Therefore 1mm² is good to go.
the value for I is incorrect mate. You need to measure the zs of the circuit, to work out the actual fault current. Higher reading the better! In your situation
 
Not quite.

You need to calculate the ACTUAL disconnection time with the ACTUAL fault current at that point. Typically a BS EN 60898 circuit breaker has an instantaneous operating time quoted as 0.1 seconds, however if you consult the manufacturer's data then there may be a definite minimum operating time of around 0.01 seconds at your value of prospective fault current at the extremity of the circuit. This could help achieve a smaller cpc csa.

Then so long as the result, i.e. S, is no greater than the cpc cross-sectional area that you have then it is adequate. This is an iterative calculation, so when designing you would have to recalculate as you increase the cpc csa as this will affect the Zs and prospective earth fault current, which will subsequently affect the size of cpc given as the minimum (i.e. it will increase - so you need to ensure that your new csa is adequate after calculation).

I agree about using the actual prospective earth fault current.

However, shouldn't it be the PEFC at the origin of the circuit? After all, the fault might occur at the nearest socket to the origin, or even in the cable before the first socket.

You might have to refer to the manufacturer's spec for I²t let-through energy and put that figure into the adiabatic equation instead of separate figures for I and t to arrive at a sensible answer.
 
However, shouldn't it be the PEFC at the origin of the circuit? After all, the fault might occur at the nearest socket to the origin, or even in the cable before the first socket.

No, because the worst case will be with the slowest disconnection time (i.e. at the extremity of the circuit). The lower prospective current at that point will cause the longest disconnection time which will thermally stress the conductors more.

In reality it can be advisable to carry out the calculation for both near end and far end faults to find the worst case, although it is generally assumed to be far end.
 
No, because the worst case will be with the slowest disconnection time (i.e. at the extremity of the circuit). The lower prospective current at that point will cause the longest disconnection time which will thermally stress the conductors more.

In reality it can be advisable to carry out the calculation for both near end and far end faults to find the worst case, although it is generally assumed to be far end.

Looks like I need to try plugging in a few figures and see how it works out.
 
Thanks guys. Juggling figures is easy! knowing what figures to juggle is the essence and this forum undoubtedly helps me understand.
I'm going back to the job this afternoon to perform the relevant tests.
I'll also look up manufacturer's specifications and respond later too.
 

Reply to Identifying csa of t&e in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
429
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top