tell them straight up.Ok so it's been confirmed, there are no previous records what so ever to refer to.
This is now a case of agreeing how I'm to go about a full test and inspection and what limitations I can agree with the client.
I'm going to suggest live testing only on all sub main supply's and anything that can't be disconnected due to production. Will this be enough to cover myself if anything was to happen after my signature goes on the whole installation?
After looking further into a few circuits coming from the main panel there are some seriously worrying things I've seen which wouldn't suprise me as to why there isn't any certs.
They have 2 lines of 6 industrial microwaves supplied from 250A IEC 60269-1 fuses straight from the main panel in 70mm SWA. That only just meets the requirements of the current carrying capacity by 1 amp and that's assuming they are laid on the tray without being bunched the whole way to the final points.
Even worse than that is that the fuses in the main panel compartments have been bodged in as the panel has been designed to isolate MCCB's.
They then go straight to the microwaves and don't have any isolators what so ever meaning the only way to disconnect them is to turn off the whole installation.
I know this is serious, and I know it needs to be sorted but the firm seem to be very tight in regards to any situation big or small (Irish run firm!).
I really need the work because I've not long set up so I need to approach this cautiously.
How would any of you more experienced sparks go about this?
do you want me to carry on with the testing, the boards and supplies to the machines dont comply.
im guessing there are no emergency stops etc either judging by what your saying.
you could argue due to derating factors the cable is not satisfactory and they should get the original contractors back to bring it upto the required specification at there cost.
its upto you how you want to go from here, personally all industrial should have some form of local isolation.
surely having to isolate the plant just to work on one machine is ridiculous especially in production.