Thanks for all the responses. Glad to see some science behind it too.

So. According to one document by calculation when using RCDs if greater than 6.66Kohms (Damien's telephone number) it is not classed as an extraneous part. If not using RCDs if greater than 22KOhms not classed as an extraneous part.

So for my scenario (using RCBOs) if the value was between 1,660Ohms and 6,666Ohms i would have to supply a bond to bring it back down to an acceptable resistance (below 1,660Ohms).

@spinlondon Do you have any reference for the NIC doc, i would like to make some notes in my regs book.

Thank you.

John
 

Reply to IEE 18th, 701.415.2 p241 - sup bonding bathroom in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
509
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
979
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
909

Similar threads

Hi I need help with understand supplementary bonding. I know RCD is additional protection and in the even of the fault at leakage of 30mA, it...
Replies
0
Views
96
  • Question
There could also be a completely unsuitable junction box embedded within the wall and tiled over or just cables in choc blocks in old accessory...
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top