Immersion faulty??? | on Free Electrical Advice - Electricians Forums
  • Please checkout the new forum categories, there is a thread about it HERE.
Discuss Immersion faulty??? in the UK Electrical Forum area at ElectriciansForums.net
Hi guys
Customer had no hot water (house has no gas, electric only)
The immersion is on an fcu with timer straight to a 18inch element.
I replaced the element after testing for a good 230v supply across live and neutral and to earth.
the customer has must phoned to say it’s still not heating up.
It’s a simple system with good supply so I’m stumped as to what it could be?
Any ideas?
the timer is ok by the way.
Hi guys
Any ideas?
Hi
I’ve changed the whole element which comes with the stat built in on top.
I would typically test the element resistance back at the consumer unit (assuming any timer can be overridden), to see a complete circuit (typically circa 18 Ohm or so) including the wiring plus any isolating switches/FCUs that might be in circuit. (Also measure insulation resistance (L+N) to E, but maybe not so relevant here). Then when power is applied, check current with a clamp meter.
But no, I would never consider changing an element, I don't do anything that involves getting wet.
Too risky. Get a plumber to change the element, you just wire it up.
out of interest, did you check across the disconnected heater for a reading in Ohms?
if it’s shorted out to zero, or totally open circuit, then it’s goosed. Should read in the tens of ohms
If you tested 230 volts directly across the element, and it didn't get hot, you could have a faulty 'stat that's switching as soon as it gets a hint of the warmed water coming off of the element. If you checked that the 230 volts was there all the time that the water was supposed to be heating, then you have a faulty element. It's not unknown for a broken element to read OK when checked with an ohm meter, but then go O/C as soon as expansion occurs when the power is applied.
Another possibility for a cylinder not heating up is a water leak on the hot system, draining the hot water faster than its produced.
The tool you should have used is a clamp meter, checking the current taken by the element.
Reply to Immersion faulty??? in the UK Electrical Forum area at ElectriciansForums.net
This is an RSS feed of thread: Two electrical supplies and a single immersion element Content of the thread: Good afternoon, new joiner here with...
Thanks all for the suggestions! Customer doesn't store anything else in the cupboard with the tank, not even towels or sheets. Heatrae stat is...
Hot water has to be stored at 60C+ and water temperature at the taps should be about 50C, If I have been told by people at work who flush and...
J
Have my water pipes been plumbed the wrong way? Good morning, I recently had an extension, new bathroom and new en-suite fitted. Prior to the...
jennys07
J
Immersion heater shouldn't be fed from a FCU it should be a dedicated circuit on a switch.