Hi guys
Customer had no hot water (house has no gas, electric only)
The immersion is on an fcu with timer straight to a 18inch element.

I replaced the element after testing for a good 230v supply across live and neutral and to earth.

the customer has must phoned to say it’s still not heating up.
It’s a simple system with good supply so I’m stumped as to what it could be?
Any ideas?
the timer is ok by the way.
 
Hi-limit cut out reset?
These are often open when you take a new immersion out of the box, especially if they're the round type,* separate from the 'stat, but that's not relevant if 230 volts was measured directly across the element terminals.

*These are the type with a small black reset button, located down between two live terminals. Customers don't tend to reset these more than once without turning the power off.
 
It could be a L or N connection failing in the Fused spur /FCU or in the consumer unit or elsewhere but making enough contact for a meter to read.

Clamping the supply to the heater is essential especially if you aren't going to wait around till it heats up and switches off.

Has it got a second switch somewhere?
 
It could be a L or N connection failing in the Fused spur /FCU or in the consumer unit or elsewhere but making enough contact for a meter to read.

Clamping the supply to the heater is essential especially if you aren't going to wait around till it heats up and switches off.
Has it got a second switch somewhere?
If their is a high resistance joint somewhere in the supply the voltage tester won't read 230 at the element. If the voltage tester is reading 230 at the element and the water does, nt start to heat after 5 Mins ( usual "hissing" noise will be heard) that the element is gone. This can be confirmed with a resistance test
 

Reply to the thread, titled "Immersion faulty???" which is posted in UK Electrical Forum on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Daily, weekly or monthly email

Back
Top