Did you actually read all of that?
All within regs to have an immersion of a 13A fuse. Millions are.A 3kw immersion heater shouldn't really be on a 13amp fuse.
A 2.5mm cable can be fried using a 13A fuse. Least is around 19A when in insulation. MCBs are superior of course.Suggesting that 24.7A could 'fry' 2.5mm seems a tad over-dramatic.
Your example of a 3kW immersion off a ring final is also an unlikely scenario. Not only does BS7671 suggest all fixed loads over 2kW be given their own circuit, but historically immersion heaters have been fed from a dedicated circuit.
If there's an actual question you'd like answered, perhaps you could ask specifically? At present it appears as though this thread is suggesting an MCB offers better protection than a fuse in circumstances which should never present themselves in reality.
A 2.5mm cable can be fried using a 13A fuse. Least is around 19A when in insulation. MCBs are superior of course.
The key to the thread is one-shot.
I have come across many.I'll respond this last time and be done, now that we at least know the reason behind your initial post.
You're taking a very limited set of circumstances and less than reasonably applying a worst case scenario to them. Would that cable be operating beyond regulatory parameters if enclosed in a thermally insulated wall? Yes it would, although that's not to suggest it would 'fry' and nor does it suggest this worst case is representative to all (or even a majority of situations).
I'll also add that, while such loads are indeed to be found supplied from ring final circuits, most were fitted long ago and no credible electrician will have considered hanging a 3kW immersion off a ring for quite a number of years. I can't think of a single instance where I've encountered a 3kW immersion supplied from a ring and that includes installations dating back to the 1950s, wired in rubber cables. Maybe standards have traditionally been higher over here (I doubt that), but every immersion I've seen has had its own circuit - even when distribution was limited to a total of four circuits for an entire property.
Many date from about 30? years ago, when the government offered free insulation top ups for the lofts of pensioners. Many of those pensioners lived in bungalows which already had 4" - 6" of loft insulation, with all the power wiring lying on top of it.I have come across many.
So you think it is safe for the end user to reset the 13A mcb because it has tripped through a high fault situation which is likely to be the cause?13A MCBs are superior in many ways to a fuse. Is there one available that cannot be immediately switched back on by the user after tripping?
Using a fuse it is best to use 10A rather than 12A to prevent a cable frying? A 10A fuse can pass 19A before blowing, so a 2.5mm cable will not fry. The fuse may get hot but decent makes of FCU have enough ventilation around the fuse to dissipate heat preventing scorching.
Read what I wrote again. It was clear.So you think it is safe for the end user to reset the 13A mcb because it has tripped through a high fault situation which is likely to be the cause?
I did you say the mcb trips I presume through a fault and it can be turned back on by the user even if the fault is still there resulting in a flash, bang from the mcb.Read what I wrote again. It was clear.
Very clear what I am on about which no one has grasped after all these posts.I did you say the mcb trips I presume through a fault and it can be turned back on by the user even if the fault is still there resulting in a flash, bang from the mcb.
I did say it could be any other appliance.An immersion heater is a fixed resistive load and is not likely to overload and any fault whether this be between conductors or to earth will result in a high current fault which will be cleared by the protective device.