View the thread, titled "Immersion fuse or MCB?" which is posted in UK Electrical Forum on Electricians Forums.
Steve-S
Deleted account
An immersion heater 3kW, say off a final ring. A number of points.
Is is best have a 13A double pole FCU switch or a double pole 13A type C MCB?
A fuse is one-shot. If it blows the danger is eliminated until seen to. The MCB in a local enclosure doubles as switch but can be switched back on by the user.
Gradual current increase on a 13A fuse can cook a 2.5mm cable before a fuse blows. This can be a dangerous yet all legal. This is not such a problem with an MCB which will trip quicker.
Any views on this welcome.
If the mcb trips it is likely the immersion needs replacing so it is not a sensible solution for the user to try and switch it back on if there is a high current fault failure, it will flash and bang.
I'm guessing this is a case of looking at options for an existing situation, but it's difficult to be certain from information provided in the opening post.
BS 1362 specifies the fusing current as 1.9 times the rated current. If the current exceeds the fusing current, the fuse must blow within 30 minutes. So a 13A fuse must blow within 30 minutes when carrying a current that exceeds 24.7A. 24.7A can fry a cable, especially when it is derrated say in an insulated wall.
MCBs are better, but a 13A fuse is a one-shot. MCBs are better for protection but can be switched back on again by the user as they are not one-shot.
I am using an immersion as an e.g., as it can be on for long periods with an ability to cook a cable while all within regs, while plug-in appliances are by design only drawing maximum current for short periods.
Suggesting that 24.7A could 'fry' 2.5mm seems a tad over-dramatic.
Your example of a 3kW immersion off a ring final is also an unlikely scenario. Not only does BS7671 suggest all fixed loads over 2kW be given their own circuit, but historically immersion heaters have been fed from a dedicated circuit.
If there's an actual question you'd like answered, perhaps you could ask specifically? At present it appears as though this thread is suggesting an MCB offers better protection than a fuse in circumstances which should never present themselves in reality.
A 3kw immersion heater shouldn't really be on a 13amp fuse.
Reply to the thread, titled "Immersion fuse or MCB?" which is posted in UK Electrical Forum on Electricians Forums.
Steve-S
Deleted account
London
Other
Steve-S,
westward10,
