Hi guys
I was called to a clients house today, because for a week they've had no hot water which is supplied by their immersion heater in the loft.
There is 230V L/N going into the timer, 230V L/N going from time to the immersion.
There is 230V L/N going into the thermostat, which is set to 60 degrees, and 230V L/N going to the elements. I turned the power supply off and disconnected the thermostat from the element. Tested the continuity between the elements with a reading of 19 ohms.
As far as I can see, the immersion should be working fine - I sat there for almost an hour with 230V going from the thermostat to the element - still no hot water.
I could hear a light clicking noise coming from inside the cylinder tank.
Has anyone come accross this before, I have no idea what the problem could be! Does anybody have any ideas.
Thank you so much guys!!!!
Kelly x
I was called to a clients house today, because for a week they've had no hot water which is supplied by their immersion heater in the loft.
There is 230V L/N going into the timer, 230V L/N going from time to the immersion.
There is 230V L/N going into the thermostat, which is set to 60 degrees, and 230V L/N going to the elements. I turned the power supply off and disconnected the thermostat from the element. Tested the continuity between the elements with a reading of 19 ohms.
As far as I can see, the immersion should be working fine - I sat there for almost an hour with 230V going from the thermostat to the element - still no hot water.
I could hear a light clicking noise coming from inside the cylinder tank.
Has anyone come accross this before, I have no idea what the problem could be! Does anybody have any ideas.
Thank you so much guys!!!!
Kelly x