Immersion tripping after new bathroom | Page 3 | on ElectriciansForums

Discuss Immersion tripping after new bathroom in the UK Electrical Forum area at ElectriciansForums.net

Joined
Feb 4, 2018
Messages
6
Reaction score
0
Location
Newbury
Hi. We have an immersion heater tank on economy 7. We have had no issues with this since moving in 3 years ago. We have just had our bathroom renovated including an electric towel heater wired in. From the very next day our night time immersion switch keeps tripping. Our decorator tells us there is no connection but it seems a large coincidence. He has tried to get the immersion out to replace it but was unable to so says the tank needs replacing. Can you please let me know your thoughts and if there a likely connection. Thanks
 
Our day switch is not tripping. We have never used it as always used the night time switch. He has suggested swapping them over and re wiring so that the night time one is then on the non tripping switch and vice versa. Would that be a good solution or is it only a quick fix?
 
The chap who did the bathroom, who has been with an electrical tester since and looked at the immersion. 1 other question too, if the day switch is not tripping, if we turned that on for 2 hours per day, how would the costs compare roughly to having the night switch on all night?
 
It would be fine to give you hot water for now Sarah but around twice as expensive to run on daytime rates. I'd say the night time Economy 7 immersion would cut out on its thermostat within a couple of hours anyway. [When working].
 
Hi,you need to say,what is tripping, Is it an MCB,the RCD,or a separate unit,protecting that circuit?

Your decorator/plumber/electrician,must have tested the element,before attempting to remove it? Or was that a guess?

I feel your trilogy of artisans,may be running you round in the circle of apathy,and you may find,employing a fresh,independent electrician,would give you a result and some professional advice to pass on.

Always remember the Latin maxim "Novamura Anaglypta Mattflock":):):)
 
The chap who did the bathroom, who has been with an electrical tester since and looked at the immersion. 1 other question too, if the day switch is not tripping, if we turned that on for 2 hours per day, how would the costs compare roughly to having the night switch on all night?

Do you mean he borrowed a tester or brought a competent spark with him?

Back to the issue, given you've had work done, then this is where any investigation should start.

As for the "off peak" circuit - to undertake proper tests on this and the actual immersion would take less than 1 hour - then you will know whats wrong.
 
I don't know what an MBA or R&D are as I'm not an electrician. The electrical switch where all the switches are (in the boxes where you turn the electricity on and off) there is one marked immersion. When we turn on the night time switch in the airing cupboard, the immersion marked switch in the electricity box flips down
 
sounds like a MCB (minature circuit breaker) tripping due to an overload or a short circuit. however, if the MCB has a test button, it incorporates a RCD . the only way to test for the fault is with something like this:
[ElectriciansForums.net] Immersion tripping after new bathroom

not something like:
[ElectriciansForums.net] Immersion tripping after new bathroom
 

Reply to Immersion tripping after new bathroom in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
265
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
756
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
746

Similar threads

Thanks all for the suggestions! Customer doesn't store anything else in the cupboard with the tank, not even towels or sheets. Heatrae stat is...
Replies
11
Views
1K
Yet another update: I believe what EDF have done is moved me from an Economy 9 to an Economy 7. I've just emailed them to ask if they can switch...
Replies
2
Views
239

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top