SparkusMaximus
Hi all,
My mother in law has a gagarage converted into an annex, a lot of bodging has taken place all before I knew them.
Inside the flat conversion we have a 9.5 kw shower on a 32a, a ring on a 32, light circuit on a 6a and a water heater on a 16a,
Now the SWA supplying this is 6mm protected by a 32a mcb on the rcd protected side of the CU.
I said I would sort it out for them as when they have the shower it will trip sometimes as they use a plug in heater.
I want to obviously change the cable, but working out my MD its looking like I need a 16mm this will be a nightmare so can 10mm be justified?
CC of 10mm swa ref method C is only 58a table 3 (three core as I need to transport the earth)
Do I need 16mm or will 10mm sufice.
Thanks guys I really appreciate your help as I want to be able to work things out the BRB way.