My mother in law has a gagarage converted into an annex, a lot of bodging has taken place all before I knew them.

Inside the flat conversion we have a 9.5 kw shower on a 32a, a ring on a 32, light circuit on a 6a and a water heater on a 16a,

Now the SWA supplying this is 6mm protected by a 32a mcb on the rcd protected side of the CU.

I said I would sort it out for them as when they have the shower it will trip sometimes as they use a plug in heater.

I want to obviously change the cable, but working out my MD its looking like I need a 16mm this will be a nightmare so can 10mm be justified?

CC of 10mm swa ref method C is only 58a table 3 (three core as I need to transport the earth)

Do I need 16mm or will 10mm sufice.

Thanks guys I really appreciate your help as I want to be able to work things out the BRB way.
 
10mm XLPE SWA has a ccc of 81A ref. method C , clipped or buried. will be adequate for your needs, ( ref. AEI Cable Finder , online )
 
Well thats what I am thinking logically, but when I do the MD it comes out at about 90a, I know they will not pull that but and a 10mm will be an improvement but, shower will be 41a although its on a 32a mcb which never trips only the the mcb in the house goes for the whole lot.

and I don't think I can put it on a 63 as the ccc is only 58 for a 3 core swa ref c or have I got that wrong?
 

Reply to Improve a bodged garage supply. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
791
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
978

Similar threads

Agreed, i have a cabin in the woods, water heating and hob is via 19Kg propane bottles, lasts ages and space heating is via warm air heaters via...
Replies
11
Views
2K
I don't really know if he is or not, but I would have thought an electrician would be able to calculate cable size or know about requirements for...
Replies
8
Views
670

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top