Hi all,
My mother in law has a gagarage converted into an annex, a lot of bodging has taken place all before I knew them.
Inside the flat conversion we have a 9.5 kw shower on a 32a, a ring on a 32, light circuit on a 6a and a water heater on a 16a,
Now the SWA supplying this is 6mm protected by a 32a mcb on the rcd protected side of the CU.
I said I would sort it out for them as when they have the shower it will trip sometimes as they use a plug in heater.
I want to obviously change the cable, but working out my MD its looking like I need a 16mm this will be a nightmare so can 10mm be justified?
CC of 10mm swa ref method C is only 58a table 3 (three core as I need to transport the earth)
Do I need 16mm or will 10mm sufice.
Thanks guys I really appreciate your help as I want to be able to work things out the BRB way.
So your thinknig is that you will need a 60amp supply to feed thse 4 circuits .................... I would say that 40 amps would be more than efficient, if you don't think it is then you could get a 50amp, but remember entirely houses run quite happily on just 60amps.
Just done a quick calc on Amtech, it is coming back at 35mm, that 9.5 Kw is the problem, plus another 13Amp heater
10mm XLPE SWA has a ccc of 81A ref. method C , clipped or buried. will be adequate for your needs, ( ref. AEI Cable Finder , online )
Well thats what I am thinking logically, but when I do the MD it comes out at about 90a, I know they will not pull that but and a 10mm will be an improvement but, shower will be 41a although its on a 32a mcb which never trips only the the mcb in the house goes for the whole lot.
and I don't think I can put it on a 63 as the ccc is only 58 for a 3 core swa ref c or have I got that wrong?
Thanks telectric I did see the XLPE thread but thought that value was only burried, didn't realise it was for ref c too.
as i said 10mm XLPE on a 63A be fine.