My mother in law has a gagarage converted into an annex, a lot of bodging has taken place all before I knew them.

Inside the flat conversion we have a 9.5 kw shower on a 32a, a ring on a 32, light circuit on a 6a and a water heater on a 16a,

Now the SWA supplying this is 6mm protected by a 32a mcb on the rcd protected side of the CU.

I said I would sort it out for them as when they have the shower it will trip sometimes as they use a plug in heater.

I want to obviously change the cable, but working out my MD its looking like I need a 16mm this will be a nightmare so can 10mm be justified?

CC of 10mm swa ref method C is only 58a table 3 (three core as I need to transport the earth)

Do I need 16mm or will 10mm sufice.

Thanks guys I really appreciate your help as I want to be able to work things out the BRB way.
 
So your thinknig is that you will need a 60amp supply to feed thse 4 circuits .................... I would say that 40 amps would be more than efficient, if you don't think it is then you could get a 50amp, but remember entirely houses run quite happily on just 60amps.
 
Just done a quick calc on Amtech, it is coming back at 35mm, that 9.5 Kw is the problem, plus another 13Amp heater
 
10mm XLPE SWA has a ccc of 81A ref. method C , clipped or buried. will be adequate for your needs, ( ref. AEI Cable Finder , online )
 
Well thats what I am thinking logically, but when I do the MD it comes out at about 90a, I know they will not pull that but and a 10mm will be an improvement but, shower will be 41a although its on a 32a mcb which never trips only the the mcb in the house goes for the whole lot.

and I don't think I can put it on a 63 as the ccc is only 58 for a 3 core swa ref c or have I got that wrong?
 
Thanks telectric I did see the XLPE thread but thought that value was only burried, didn't realise it was for ref c too.
 
as i said 10mm XLPE on a 63A be fine.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Improve a bodged garage supply.
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
33

Advert

Thread statistics

Created
SparkusMaximus,
Last reply from
malcolmsanford,
Replies
33
Views
3,436

Advert

TrueNAS JBOD Storage Server

Back
Top