cut out 100a, main switch in CU 100a, but was thinking of putting in a little 1 way garage supply, However I think I will jsut keep it in the mian C/U.
Not for inductive loads like showers or water heaters as a final circuit, but when we are doing an installation like this with other types of circuits then I would take diversity into account ................otherwise most modern homes would be having 150+amps supplies to them all.
quite right I have inductive on the brain ................... unless the shower as a big motor pump in it ...........teach me to be working on motor design and skiving off on here
cut out 100a, main switch in CU 100a, but was thinking of putting in a little 1 way garage supply, However I think I will jsut keep it in the mian C/U.
To be honest if I don't like putting 50amp or 63amp MCB into a domestic board, IMO it is loading them up.
I would personally henly block the tails from the meter to the CU and fit a 60 amp switch fuse and if you wanted to you could fit a smaller fuse. Then run your 10mm^ SWA into a small garage CU with a 63amp 30mA RCD protecting the circuits there.