ExArmy

-
Joined
Jul 27, 2010
Messages
716
Reaction score
143
Location
cumbria
I have just been to look at a job where i was asked to install a cooker as the previous one had nearly burned the house down apparently. when i took the cooker out there was a large burnt patch (300m accross), loads of charcoal, almost got through 1/2" ply below . when i pulled out the heat resistant flex i couldn't see where it had been plugged into, but it's likely it was plugged into the ring. it is a 3200W cooker from argos, the customer had got an argos technician out and apparently the cookers fine and it was down to the installation. customer reckons it was sat ontop of the connections and it was bodged up, I did try asking the customer to clarify how the cooker was connected up, but couldn't get much out of her! theres a 2.5 T&E running below the worktop behind the cupboards, not connected to anything but still live? but couldn't find where it came from as all the cupboards are full to the brim!

it's only a small house, 2 up 2 down, it's TT, got a 100mA RCD upfront and a 8 way 3036 board with 3 circuits (ring, lights and shower). ZE is 5-6ish ohms. would it be ok to spur it off the ring to a fused spur above the worktop, and then down to the cooker? an just put it on a minor works?
I'm not entirely sure what the line is about working on a circuit without 30ma RCD protection, do i need to add an RCD first or not?

also, the voltage is 250V at this house, 3200W at 250V is 12.8, so it i put a 13A fuse in the FCU then it will be alright? i seem to remember something from college saying all calculations to be worked out at 230V, in which case the current will be 13.9A and it will be more than the fuse rating. probably never blow, but what should i do here?
 
the board is the opposite side of the house to the stop cock and the gas meter and theres no bonding. and the house is a tip, and dirty.
Didn't know you'd been round here, should have stayed for a brew... :)
 
No bonding ??
lol , then youre not going to be doing any work till that sorted.
if i was you i'd just price mself out of the job , sounds a whole load of hassle unless the customer is gonna pay for all the extras.
 
so if i was to fit a new board, i'd have to fit a 100mA time delayed RDC main switch? also i would fit bonding, and what about the main earth to the erath spike? it's 10mm at the minute, dissapears into the wall and i can't see where it goes. how do i go about fettling this upto the 17th edition, and how do I test it?
 
No bonding ??
lol , then youre not going to be doing any work till that sorted.
if i was you i'd just price mself out of the job , sounds a whole load of hassle unless the customer is gonna pay for all the extras.

Have you weighed the client up yet? Judging a book by it's cover is never good (and sometimes it goes wrong) but is there money in it for you? Are they likely to go for it OR are could this be a factor as to how they ended up with a shoddy job done in the first place?

If in doubt price yourself out of it and walk away:thumbsup
 
No bonding ??
lol , then youre not going to be doing any work till that sorted.
if i was you i'd just price mself out of the job , sounds a whole load of hassle unless the customer is gonna pay for all the extras.

yeah thats looking like the option i'm leaning towards, i'll do the EICR and then whack in a sky high price...
 
so if i was to fit a new board, i'd have to fit a 100mA time delayed RDC main switch? also i would fit bonding, and what about the main earth to the erath spike? it's 10mm at the minute, dissapears into the wall and i can't see where it goes. how do i go about fettling this upto the 17th edition, and how do I test it?

No need to fit a 100mA TD upfront, provided the CU you replace it with is Class II (plastic) and at least a Dual RCD split load, see OSG p16 Fig 2.1(iii).
 
Have you weighed the client up yet? Judging a book by it's cover is never good (and sometimes it goes wrong) but is there money in it for you? Are they likely to go for it OR are could this be a factor as to how they ended up with a shoddy job done in the first place?

If in doubt price yourself out of it and walk away:thumbsup

yes, the person paying for the work is the landlord, who owns several properties, and the people who bodged the cooker have worked on his houses for years and never had any problems before (nothing short of a miracle from some of the wiring i saw today) i'll get some pics on my periodic tomorrow
 
so if i was to fit a new board, i'd have to fit a 100mA time delayed RDC main switch? Yes

also i would fit bonding, Yes
and what about the main earth to the erath spike? it's 10mm at the minute, Needs to be 16mm
dissapears into the wall and i can't see where it goes. You need to find and check the rods condition , but it sounds like its giving good readings from your earlier posts.

how do i go about fettling this upto the 17th edition, and how do I test it? Use earth loop test from CU main switch terminals and earth rod conductor.

.........................
 
Why does he have to fit a 100mA TD upfront RCD Biff ?, if he replaces the CU with a plastic Dual RCD one there is no reg that says you must fit an additional Upfront TD 100mA RCD.

I Know some sparks have their own preference on this, as I would consider it in certain circumstances, but on such a small domestic install I wouldn't bother.

Likewise on the earthing conductor, so long as the cable isn't buried he could use 6mm, in fact if it was mechanically protected it is possible to use 2.5mm on a domestic TT (not that you would).
 
And just as i thought we might be getting near the end of this long journey lol.

Hey it's only stating I disagree ;) I'm not trying to start an argument over it lol

Perhaps I have typed before engaging brain but I do not come across many TT installations so perhaps you know something I do not? If so I would be more than happy for someone to enlighten me and I will stand correct. We've got 6 minutes for me to learn something new today:thumbsup

Make that 5 :D
 
Why does he have to fit a 100mA TD upfront RCD Biff ?, if he replaces the CU with a plastic Dual RCD one there is no reg that says you must fit an additional Upfront TD 100mA RCD.

I Know some sparks have their own preference on this, as I would consider it in certain circumstances, but on such a small domestic install I wouldn't bother.

Likewise on the earthing conductor, so long as the cable isn't buried he could use 6mm, in fact if it was mechanically protected it is possible to use 2.5mm on a domestic TT (not that you would).

I stand corrected with the point of not needing 100mA if dual 30mA ( im blaming it on the liquor lol )
However if he cant prove the rod earth conductor is mechanically protected when buried ( and i bet its not ) then 16mm is required.
 
i said this evening i'll have to RCD protect anything i fit which would mean changing the board,


Stand alone Rcd
It will certainly make you more competitive than John from the Pub,that's comparing to the proposed all singing and dancing 17th compliant and possibly un necessary new board
 

Reply to in after a cowboy, cooker nearly burnt the house down! in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
257
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
739
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
721

Similar threads

  • Question
Obviously not a building/DIY forum so will keep it short but yes - we've taken all the floors up. Several joists in the bathroom need doing as...
Replies
8
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top