I don't think you have a fault or an overload issue, you say in the OP that you have thermal overload relay if it was an overload issue then that would pop.

Also if it was overload the 16amp would pop first. Unless as was suggested you have a myriad of other things coming off that 40amp MCB that when the router starts up takes it over the top......then you have some issue with the 40amp breaker

It may very well be a dodgy breaker, it as been known that new accesories fail.

Try fitting the fuse, honestly my post about it was a little tongue in cheek, but I stand by that unless there is a reason not to I would always design a distribution circuit with a fuse
 
I don't think you have a fault or an overload issue, you say in the OP that you have thermal overload relay if it was an overload issue then that would pop.

Also if it was overload the 16amp would pop first. Unless as was suggested you have a myriad of other things coming off that 40amp MCB that when the router starts up takes it over the top......then you have some issue with the 40amp breaker

It may very well be a dodgy breaker, it as been known that new accesories fail.

Try fitting the fuse, honestly my post about it was a little tongue in cheek, but I stand by that unless there is a reason not to I would always design a distribution circuit with a fuse



It was miss-information on behalf of the lad i'm doing the job for.. when he contacted me he said it was the breaker in the main DB that was tripping.. when i went up today i found out it was actually the local sub-board 16A MCB that was tripping because of the in-rush current .. I had a spare 32A Type C so i put that on and it fired up fine.. I'm either going to order a 16A type D or a 20A type C .. the Thermal overload is set to 16A so i'm quite happy to go up to 20 on the MCB as i'm dubious about the type D doing the job.. what do you think?
 
What is the EFLI? This will determine what mcb may or may not be fitted with the existing cables.

Earlier in post you said it was supplied with a 32A commando plug fitted and instructions to fit a 32A socket etc and set overloads to 16A, to my mind this suggests they are expecting you to fit a 32A supply.
 
Did you check the motor plate for the FLC ... I'm still scratching my head here about a 3ph 3kw motor will a FLC of 16amp?

Motor Current Charts

Check the 3ph (2nd chart) - you're looking at approx 6.5flc for a 3kw, if it runs at 6 then that sounds about right, the 16amp I would suggest is the mcb rating although incorrectly specified as it should be a 20amp B or C on a standard 3kw 3ph induction motor with a normal starting duty.

If this motor had an FLC of 16amps then it would be in excess of 7.5kw rating - so be careful when choosing the correct motor overload device, you have already been given the wrong info once.
 
Last edited by a moderator:

Reply to In-Rush Issue ? in the Commercial Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
949
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Just re-read the OP's post and it is an existing 5C SWA so presumably a 3P supply. For 40A and 150m you are seeing 6.6V drop or 1.65% of 400V 3P...
Replies
8
Views
890
A picture paints a thousand words so here's an SLD showing my installation and some annotations to show the proposed relocation of the DC...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top