Incorrect SWA glanding/bonding | on ElectriciansForums
Discuss Incorrect SWA glanding/bonding in the UK Electrical Forum area at ElectriciansForums.net
Chelmsford
Hi all,
I've just moved into a rented property and found the attached photo outside the conservatory. It spurs from an inside socket and goes down the garden to an outhouse. I've tried using the 18th edition to find some evidence that this is obviously the incorrect method, as I'd like to go to the agent with some good evidence.
There's also no RCD protection as the house has the old Wylex fuses.
Can anybody find something in the regs book that I could use? Is this even a pass on an electrical certificate?
Cheers all.
[ElectriciansForums.net] Incorrect SWA glanding/bonding
That's incredibly poor workmanship section 526 Electrical connections
RCD is a requirement too since it is highly likely to be used outdoors too 411.3.3
Where is that "Earth" attached to the Armour going?
It's not encased in wood, it's a metal board. It's the plastic boards of that age which had a wooden backing plate.
Oh I meant the closure around the entire incoming supply, not the ccu.
[automerge]1575834639[/automerge]
The main switch is an rcd hard to make out if it is 30ma but probably is. Press the test button see if it trips.
It's 100ma and yes it does trip everything.
Makes you wonder why some folk even bother with SWA in the 1st place.
At least the armour is earthed, that's not always the case!
the outside sockets must be protected by a 30mA RCD. There’s a 100mA, so that’s downright dangerous and does not comply.
I agree, disconnect until it’s done properly.
Reply to Incorrect SWA glanding/bonding in the UK Electrical Forum area at ElectriciansForums.net