Guest viewing limit reached
But what if the OP is converting 2 radials to a RFC? That would be creating a new circuit.
I can see where you are coming from, but me personally, a new circuit that I sign of as new is new cable from the DB. I would consider it a modification and in this case it maybe a broken ring but OP has not confirmed rn & r2 yet AFAIK. Out of interest, would you genuinely notify on this.... really?
Dave, I can see your point too, but is it really new? Also, out of interest, would you personally notify on this one?
Yes I would notify and have in similar circumstances.
To be specific when finding a fault on a ring and converting to 2 x radial ccts by disconnecting the damaged cable where raplacement was not feasable. I converted it to 1x20A radial and 1x 16A radial, as far as I am concerned that is 2x new ccts.
Ok, fair enough. If OP's situation turns out to be broken ring and he rectifies break and installs 32A MCB, would you notify that?
If it's a like for like replacement no, same route same size cable . But the OP hasn't confirmed anything yet.
Yes, I would notify. Because:
Section 0, Table 1 (Work that need NOT be notified)
Notes -
(a) On condition that the replacement cable has the same current-carrying capacity and follows the same route
(b) If the circuit's protective measures are unaffected
By reconnecting the two cables to create a RFC you directly affect (a) and in changing the OCPD you affect (b).
Now, before you all jump on the bandwagon and make comments about the specific lines those notes refer to, I think it's fairly clear what is actually meant, even though as badly worded as you'll usually find in any Government document.
It's not like for like! It's changing a 20A OCPD for a 32/30A OCPD with completely different Zs limits to comply with ADS.
Besides......it's £1.50 and few seconds online - is it really THAT big a deal to notify it just to be safe???
Safe from who or what???? Why don't we just notify every job we do just to be safe. Tests and competence provide safety, not a notification. This may well just be a broken ring that is to be repaired. Test and certification definatly.
Safe from accusations of failing to notify work.
I can't remember the exact wording at the moment but I think the terms and conditions of ELECSA registration are that all jobs must be registered with them via their notification system, I don't think they specify that you only register part p notifiable jobs.
But in any case nobody bothers to police part P so just take the money and get back on Tonto!
london
Increase mcb capacity. Notifiable?
spynage,
Dan,
