Ive been asked to install a new circuit for an induction hob. The customer doesnt have the appliance as of yet but after a little bit of searching i managed to find the technical info i was after. The total load is stated as 3.68kw, but it also states that there are 2 x burners rated at 1.4kw and 2 others rated at 1.8kw. Obviously adding the burners together gives me a rating much bigger than the 3.68kw stated. As the kitchen is due to be plastered this week i need to get my first fix done for this circuit and was just wondering whether to cover my arse with a cable big enough to take the load of the 4 x burners or whether a diversity factor has been applied and i should just work of the 3.68kw total load.
 
Although you havnt really helped have you, where do you get your 10kw from. Is this the 4 x burners added together with the 3.68kw total load? If so why isnt the total load stated as 10kw? All youve done is try to be cocky and completely missed my my point with your accusations, i can only assume you know everything with such an attitude.
 
whether a diversity factor has been applied and i should just work of the 3.68kw total load.

By my calc assuming the full load is ~ 10kW @ 230V = 43A. With diversity = 10A + 30% (43 - 10) + 5A for a socket if fitted ~ 25A

I doubt whether 3.6Kw includes diversity as this equates to ~ 16A. The only thing I can think of is does the cooker allow you to run everything at once? Some limit the total load that can be applied at any one time so maybe thats what the 3.6kW refers to?

If in doubt give the manufacturer a tinkle ......
 
Although you havnt really helped have you, where do you get your 10kw from. Is this the 4 x burners added together with the 3.68kw total load? If so why isnt the total load stated as 10kw? All youve done is try to be cocky and completely missed my my point with your accusations, i can only assume you know everything with such an attitude.

So what size cable are you going to put in then?
 
Although you havnt really helped have you, where do you get your 10kw from. Is this the 4 x burners added together with the 3.68kw total load? If so why isnt the total load stated as 10kw? All youve done is try to be cocky and completely missed my my point with your accusations, i can only assume you know everything with such an attitude.

So what size cable are you going to put in then?
Given my uncertainty over the total load and the fact that i have a little bit of cable on my van going spare going for 6mm2, after all what will do a lot will do a little. Its just about covering my arse as i initially stated and was after people opinions on whether they would also err on the side of caution, given the time restraints on the job. What i got was sombody questioning my ability and trying to teach me how to suck eggs.
 
The thing is pepparz i only wanted help with what i have interpreted as the total load. I am quite capable to work out the correct size of cable once known. People are to quick to jump on you on here, take the moron who was first to reply for example.
 

Reply to induction hob cable size in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
172
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
542
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
489

Similar threads

  • Question
If your using 35mm or 50mm use 2 core SWA and use the armour as the earth, it'll cut down on price. I know people will comment on this but the...
Replies
10
Views
1K
  • Question
Hello oscar21, When I wrote about cables heating up I meant that IF a cable heated up that heat could not dissipate correctly if the cable was...
2
Replies
16
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top