Octopus
Sorry for the juvenile drawing. It's something like this:
View attachment 47023
If its like that you need to rip it out and have it done properly
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Induction hob wiring in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Sorry for the juvenile drawing. It's something like this:
View attachment 47023
The hob should be OK to be connected in with the 32A supply for the oven using the first diagram with the L1 and L2 teminals linked and the N1 and N2 terminals linked.
To have to independently isolated supplies to one appliance could be confusing and dangerous because if someone was working on a faulty part, isolated a single switch and found the faulty part was off, they could then start opening up the equipment not realising there was still a live supply present, though they would have to be missing out on a lot of standard safety practice.
The house ring looks like there are a lot of potentially overloaded cables there and this should be addressed by rearranging the wiring to form a single ring.
The hob should be OK to be connected in with the 32A supply for the oven using the first diagram with the L1 and L2 teminals linked and the N1 and N2 terminals linked.
To have to independently isolated supplies to one appliance could be confusing and dangerous because if someone was working on a faulty part, isolated a single switch and found the faulty part was off, they could then start opening up the equipment not realising there was still a live supply present, though they would have to be missing out on a lot of standard safety practice.
The house ring looks like there are a lot of potentially overloaded cables there and this should be addressed by rearranging the wiring to form a single ring.
Please DO NOT connect a single load to 2 circuits - a VERY bad idea, and extremely dangerous
I thought 1.13 times the rating was indefinite, with 1.45 times the rating operating within conventional time (1 hour).In accordance with the standards on domestic circuit breakers a circuit breaker must be able to carry 1.13 times its rated current (36.16A) for at least one hour.
The thermostats on the heating elements will cut in and lower the power draw well before that point.
Yes, at 1.13 times it must not operate within one hour, at 1.45 times it must operate within one hour. I do not know of a time requirement for tripping at 1.13 times only for not tripping. Though I could be wrong.I thought 1.13 times the rating was indefinite, with 1.45 times the rating operating within conventional time (1 hour).
Reply to Induction hob wiring in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net