Bogart

-
DIY
Joined
Aug 19, 2019
Messages
32
Reaction score
2
Location
NR14 8JB 5 miles sw of Norwich
Am about to install an induction hob and can either use single phase or three phase. Will use singles in conduit. Maximun load is 11Kw so either single phase in 6mm or 3phase using 2.5mm. If I use 3 phase I will get a normal cooker isolation switch to operate a 4 pole contactor, as am not too keen on an industrial looking switch by the hob!

Is there any overiding reason I should use one over the other?
 
In the same way a light switch isn't considered isolation.

Most contactors, unless "safety rated" don't have the required gap distance between contacts to meet isolation rules.

Also bear in mind, it would break the N at the same time as the lines, really lines need to break first, and connect last.
 
In the same way a light switch isn't considered isolation.

Most contactors, unless "safety rated" don't have the required gap distance between contacts to meet isolation rules.

Also bear in mind, it would break the N at the same time as the lines, really lines need to break first, and connect last.

So tell me how does a normal cooker switch "isolate" the appliance?
I can see nothing wrong in using a 4pole NC contactor. Only need an isolator switch in case of emergency and in that case as long as the lives and neutral are opened fine. As there is no actual electrical reg requirement for local isolation of an appliance I cannot see why my suggestion is not valid.
 
So tell me how does a normal cooker switch "isolate" the appliance?
I can see nothing wrong in using a 4pole NC contactor. Only need an isolator switch in case of emergency and in that case as long as the lives and neutral are opened fine. As there is no actual electrical reg requirement for local isolation of an appliance I cannot see why my suggestion is not valid.

A normal cooker isolator puts a gap in the circuit of a set amount. There is a difference between functional switching and switching for isolation. However a functional switch in some circumstances can be both, an MCB for example.

Also, if you are going down this route, you'll want a normally open contactor. This way, if it fails, it is more likely to fail in a safe manner.
 
Hi - my 20p is that a contactor will always be on, consuming a few Watts and possibly buzzing. So I wouldn’t use one for a domestic cooker. I’d try for a rotary switch in an adjacent cupboard.
 
A 4 pole NC contactor fed from a switch on the wall is about as far away from a safe means of isolation as I can imagine.

If you had an engineer round to fix a problem and the turned off the isolation switch, they would expect that there would be no way it could become energised again without them operating the switch.

However, if the coil failed or any of the control wiring was disturbed and became separated the cooker would become live again. There are so many ways this could go wrong.

You can get some reasonably small and neat 3 phase isolator, you don’t need to get some plastic rotary thing with a yellow handle.
 
just fix this in the adjacent cupboard, or.... if you want to annoy the wife, fix it in plain sight. Tell her it's 18th Ed. regs.
[ElectriciansForums.net] Induction hob.
 
A normal cooker isolator puts a gap in the circuit of a set amount. There is a difference between functional switching and switching for isolation. However a functional switch in some circumstances can be both, an MCB for example.

Also, if you are going down this route, you'll want a normally open contactor. This way, if it fails, it is more likely to fail in a safe manner.
Only problem with a NO is that it will be constantly powered up unless one switches it off after every cooker use.
 
Am receiving conflicting advice as to local isolation. Is a cooker as such required to have a local isolation point or is say the MCB in the CU good enough?

It seems wise to have local isolation near to a cooking appliance.
 

Reply to Induction hob. in the DIY Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
450
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Has the cover been removed, is it TP bussbar? I fitted one as @oscar21 linked to a few months ago, it was actually a nice board and with the TP...
Replies
5
Views
664
I am confronted by people with experience in using them for lighting circuits and sockets in a three-phase installation, as it is only allowed to...
Replies
0
Views
193

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top