And one more question . Is there anything to stop me running the hob in 3 phase even though I have 3 CU each on a different phase? I was intending having a 20 Amp MCB in each for the hob. The hob is split into 3 zones so I
assumed, rightly or wrongly , that this was permissible.
 
And one more question . Is there anything to stop me running the hob in 3 phase even though I have 3 CU each on a different phase? I was intending having a 20 Amp MCB in each for the hob. The hob is split into 3 zones so I
assumed, rightly or wrongly , that this was permissible.
Wrongly.

You need to be able to isolate or switch off instantly at the same time.
Even more important is disconnection in the event of a fault.
 
to summise,

Yes you do need to be able to isolate the supply
reg. 464 + 537

also, being a hob that could start a fire if it were to overheat,
reg 465 would apply.

just to make life simple and easy, get a spark in and they will do all the worrying about compliance with the regs (30 seconds thinking time)
then put in a supply that is both safe and functional.
 
Diversity , you have never seen my missus cooking. The hob has a total of nearly 16kw of cooking area but the load is limited by the hob to 11kw so the total current could be around 50A so a 32A circuit not exactly ideal. Hence my wanting to spread it over 3 phases.
 

Reply to Induction hob. in the DIY Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
957
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Has the cover been removed, is it TP bussbar? I fitted one as @oscar21 linked to a few months ago, it was actually a nice board and with the TP...
Replies
5
Views
645
I am confronted by people with experience in using them for lighting circuits and sockets in a three-phase installation, as it is only allowed to...
Replies
0
Views
183

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top