Hi,
As you might remember from the last thread, I'm now working in a factory where they used to contract out the electrics.
Unfortunately they used a negligent installer, so I have to fix it with no expenditure or time taken =-)
This problem is one of the main tank rooms.
There are a selection of stirring tanks, and a pump at the bottom.
The feed to each tank and pump is separate, with it's own isolator.
Each circuit has it's own overload.
Sounds alright so far, unfortunately:
There is no CPC to any of the tanks (SY sheath does not count in my books)
There is no equipotential bonding anywhere (this room is a high risk environment, it needs it!)
The only protection for short circuit or earth fault (apart from the overload which I assume will not trip in time) is a lone D50 breaker that covers everything.
All wired in 1.5mm (fun for a D50 breaker).
So my top priority is to make it safe, then legal.
I am putting in-line fuses for all to get the SC and EF protection, but the CPC problem is an issue.
I have read guidance note 8, regs and OSG and it is so vague.
If I had designed it each circuit would have it's own dedicated CPC, but pulling out all the SY and refitting would not be allowed, and strapping CPCs to the side of the SY has been managment vetoed too.
So my idea is to link the tank CPC to the Pump to allow it to carry the fault current. On the link I am also bonding it to a metal frame that goes to near the board and that is connected too.
The way I see it is any fault on the motor will dump current through the pump CPC and the parallel path through the steelwork (Steel CSA 40mm2).
This is a photo of what I have done (I'm sorry it looks so bad, we have damaged boxes and no budget to replace them or even get stuffing glands!)
As you might remember from the last thread, I'm now working in a factory where they used to contract out the electrics.
Unfortunately they used a negligent installer, so I have to fix it with no expenditure or time taken =-)
This problem is one of the main tank rooms.
There are a selection of stirring tanks, and a pump at the bottom.
The feed to each tank and pump is separate, with it's own isolator.
Each circuit has it's own overload.
Sounds alright so far, unfortunately:
There is no CPC to any of the tanks (SY sheath does not count in my books)
There is no equipotential bonding anywhere (this room is a high risk environment, it needs it!)
The only protection for short circuit or earth fault (apart from the overload which I assume will not trip in time) is a lone D50 breaker that covers everything.
All wired in 1.5mm (fun for a D50 breaker).
So my top priority is to make it safe, then legal.
I am putting in-line fuses for all to get the SC and EF protection, but the CPC problem is an issue.
I have read guidance note 8, regs and OSG and it is so vague.
If I had designed it each circuit would have it's own dedicated CPC, but pulling out all the SY and refitting would not be allowed, and strapping CPCs to the side of the SY has been managment vetoed too.
So my idea is to link the tank CPC to the Pump to allow it to carry the fault current. On the link I am also bonding it to a metal frame that goes to near the board and that is connected too.
The way I see it is any fault on the motor will dump current through the pump CPC and the parallel path through the steelwork (Steel CSA 40mm2).
This is a photo of what I have done (I'm sorry it looks so bad, we have damaged boxes and no budget to replace them or even get stuffing glands!)