Hello all,
Trained years ago, not done much for about a decade but I've been asked by a friend to add 5x double sockets into an industrial unit, my thinking is to use a radial 32A RCB, 4mm 3-core SWA cleated to the wall (moderate impact risk). Area is small, only about 2-3m from the distribution board and there is no need for any spurs etc. I don't have a bender etc any more so don't fancy metal conduit. Appliances are almost all (very) inductive so C-curve.
I did do 18th in 2020 but haven't got a book handy, sorry if this is an egg-sucking question but can't recall current regulations for running radials. Not something I've done for several years and I recall 'something' had changed. Used to be 20A/2.5/50m2 if I recall but I know thinking has changed(?).
Cheers,
Ben
Trained years ago, not done much for about a decade but I've been asked by a friend to add 5x double sockets into an industrial unit, my thinking is to use a radial 32A RCB, 4mm 3-core SWA cleated to the wall (moderate impact risk). Area is small, only about 2-3m from the distribution board and there is no need for any spurs etc. I don't have a bender etc any more so don't fancy metal conduit. Appliances are almost all (very) inductive so C-curve.
I did do 18th in 2020 but haven't got a book handy, sorry if this is an egg-sucking question but can't recall current regulations for running radials. Not something I've done for several years and I recall 'something' had changed. Used to be 20A/2.5/50m2 if I recall but I know thinking has changed(?).