Industrial Unit Earthing Arrangement - Lack of | on ElectriciansForums

Discuss Industrial Unit Earthing Arrangement - Lack of in the Commercial Electrical Advice area at ElectriciansForums.net

Joined
Aug 20, 2018
Messages
21
Reaction score
7
Location
Cornwall
We’re in the process of replacing the 3 phase installation in our premises, the electrician that came said we should contact Western Power and request a PME, Western Power have said they can’t, we have also asked if they can supply a main earth terminal for us to connect to - they say they can’t.
Currently the only earthing arrangement we have is as follows:
Main bonding from cold water pipe goes to terminal in 3 phase isolator, 3 phase and single phase board has 10mm earth to isolator.
There is no earth from the isolator to anywhere, guess it just uses the SWA of the main incoming 3 phase cable that comes into the isolator.
Electrician says there should be a MET near our incoming supply with a 25mm earth cable from there to the isolator and I presume onwards to the new 3 phase board.
He did say something about using an earth rod if it was a house but thought it a bit impractical due to the size needed for our supply given we are on a concrete and tarmac industrial estate.
Can I have some advice please before I speak to him again.
 
We’re in the process of replacing the 3 phase installation in our premises, the electrician that came said we should contact Western Power and request a PME, Western Power have said they can’t, we have also asked if they can supply a main earth terminal for us to connect to - they say they can’t.
Currently the only earthing arrangement we have is as follows:
Main bonding from cold water pipe goes to terminal in 3 phase isolator, 3 phase and single phase board has 10mm earth to isolator.
There is no earth from the isolator to anywhere, guess it just uses the SWA of the main incoming 3 phase cable that comes into the isolator.
Electrician says there should be a MET near our incoming supply with a 25mm earth cable from there to the isolator and I presume onwards to the new 3 phase board.
He did say something about using an earth rod if it was a house but thought it a bit impractical due to the size needed for our supply given we are on a concrete and tarmac industrial estate.
Can I have some advice please before I speak to him again.
Yes, get a different Electrician
 
Where's that 'main incoming cable' coming from?
Being swa….is it an authority cable or a sub main?
 
Pictures here hopefully, here’s the cut out and isolator in the distribution room which happens to be on the opposite side of the wall to our unit, and the internal view of our isolator switch in the unit.

[ElectriciansForums.net] Industrial Unit Earthing Arrangement - Lack of

[ElectriciansForums.net] Industrial Unit Earthing Arrangement - Lack of

[ElectriciansForums.net] Industrial Unit Earthing Arrangement - Lack of
 
The isolator switch that is open is in our unit, the 3P & N supply cable in the top is from the DNO isolator next door in the meter room, the grey bit on top of the switch is not trunking - it’s the cover for the rewireable fuses on the single phase board, the 3 phase board has been removed from our unit hence no cables on the outgoing RYB phases, the single phase tap off the yellow is to a single phase rewireable fuse consumer unit, the earth cable you can see in the bottom comes from said single phase consumer unit, which incidentally is where the main bond to the cold water pipe is, the hot water currently has none nor does the steel mezzanine floor.
Managed to get hold of our chap but he can’t get out until Monday so I’m interested in any advice before then, I know it’s difficult, here’s a shot of what’s in the unit - the 3 phase panel has now gone as it was snagging the stairs

[ElectriciansForums.net] Industrial Unit Earthing Arrangement - Lack of

[ElectriciansForums.net] Industrial Unit Earthing Arrangement - Lack of
 
Last edited:
Best advice is to get an EICR done.

Best get a different electrician as I am not confident the one you are talking to knows what he is on about.
 

Reply to Industrial Unit Earthing Arrangement - Lack of in the Commercial Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
351
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
900
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
I'm assuming the cable will have to be cleated well to hold it in place anyway, as a stuffing gland ain't going to hold it tight like a SWA gland...
Replies
10
Views
710
They do a cy type with pur coating and it is even tougher but is shielded
Replies
3
Views
400

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top