Inrush currents and solutions...... | on ElectriciansForums
Discuss Inrush currents and solutions...... in the UK Electrical Forum area at ElectriciansForums.net
Dobes_88
Surrey
Good evening!
Wanting to pick the brains of people more experienced in this field, approaching 2nd fix stage of an ongoing rewire where the client wants a shed load of lights throughout.
What particularly worries me is the hallway and kitchen grid switches where there’s around 10-12 lights operated by numerous switches in each area… And he may want a couple more lights added to it!
The plan is to fit fixed Enlite E8 downlights throughout but worried about the dreaded inrush currents, have emailed Enlite to see what sort of figures I should be expecting per unit but no reply as of yet…
Would a better plan to fit LED GU10’s to limit the inrush?
It’s all wired in 1.5mm, clipped direct with switch drops in oval conduit so will be able to get away with a C10 (if Zs in limits), but with the shear volume of lights (around 25-30 x per lighting circuit) I’ve read about these inrush current limiters that could be the solution - but I haven't or know of anyone that has installed them.
Any guidance would be greatly appreciated!
I'm not domestic mate but I'm interested in the outcome to this.
A mate at work who had more wattage in his kitchen than I had in my entire house, GU10's, and never had a problem with inrush.
Would there be significant inrush if they are "operated by numerous switches"?
Haven't fitted anything yet, Consumer unit to be installed early part of next week and hopefully have the lights up and running towards the end of the week.
Initial thoughts is certainly a C6 or C10, will have to see what the Zs is first.
Just looking into possible solutions should the C type MCB not work, rather than flicking everything on and hoping for the best!
You can buy inrush current limiters. However I think it is overhyped the problem with inrush currents. I have fitted LED panels in numbers that suggest very large inrush currents and the 10a mcb (type B) has been fine. I watched a great vid on this and they simulated the process of inrush on a specialised test rig. What it showed is the distance between the lights causes the inrush to be staggered as we are talking a peak inrush current for 500 ms only. Hence the problem is ameliorated. It is very much to do with the controller so you can look at the Inrush current for most controllers on the manufacturers site. If you do fit a limiter it should be before the switch and the switch should be rated as high as you can as it is the sacrificial part of currents. There have been cases of switches and contactor/relays welding together in these situations. So it is something to be aware of. But the LED panels I put in have been going for five years without any problems.
Reply to Inrush currents and solutions...... in the UK Electrical Forum area at ElectriciansForums.net
What is the distance from the point outside the house to the shed?
Hi Gingerrubix, The fact that your previous Tenant replaced a faulty socket plate which he used for an external EV, raises an eyebrow. Also your...