Install cert required if eicr has been done | Page 2 | on ElectriciansForums
Discuss Install cert required if eicr has been done in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
The eicr being a report on a existing installation will reference the protective devices that exist at the time of inspection,renew the board and its all changed
You are required by the regs to issue certification for all installation work carried out,this can be in the form of a minor works or a installation certificate
Reporting the condition of a installation that has been altered can in no way absolve you from the breaking of the regulations by not issuing certification
Reports and certificates are 2 different animals
The reason we issue EICs when changing CUs, is because BS7671 requires us to do so.
Failure to issue said EIC would mean that the work does not comply with BS7671.
The reason people record test results for the existing circuits when they change a CU, is because they like to fill in all the blank boxes.
Of course if changing the CU entails replacing or installing RCD/RCBOs, then tests of the RCD/RCBOs will be required.
An eicr first to find out whether your installing a board to supply a load of circuits that are dangerous or can cause nuisance tripping etc
Why? After basic testing and checking before changing a CU, the installation becomes an EIC. If the client doesn't want a full test you just record it and advise one.
I do installation certs for new board changes. I’m not looking for some robot to quote regs at me. By replacing the cu with an rcd board i am improving the safety so why?? Do i have to do the same test again to get the same results
If you've already done a full EICR on the property, the only additional tests apart from identifying the new circuit layout would be the RCD tripping times. As you would have already recorded test results from your previous inspection
same results only difference is rcd times. All im saying is does no one else think its a bit overkill to do the tests again. Regs are just a guide not an act
Repeating the tests is a different matter entirely to your original question, which was do you need to issue an EIC, which you do if your installation is to be compliant with the regulations.
If of course you just view the regs as a guide and are not to be followed then you have wasted your time by even asking this question in the first place. Just carry on as you feel and ignore the regulations.
Reply to Install cert required if eicr has been done in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
As the cable itself has had the cpc cut off at both ends I would enter a C3 as it doesn't offer any protection within the cable if accidentally...
That is what i am going to do. Thanks mate!