OP
dmelec
Just easier to terminateWhy run a separate earth?
Discuss Installing 3 Phase supply to new 5/6 Bed house in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Its a big 5/6 bed house, with a few outbuildings. 80 amps is probably a slight overkill hahaThat's some house that needs 80a per phase?
Not sure how this wouldn't meet any technical standards as i would run a 4 core armoured with a sufficient separate earth?How is it easier to terminate?
Do you really think that laziness is a good basis for design over any technical or regulatory considerations?
I would not run a seperate earth just because its easier to terminate and over that length of run , but it would help get your zs down , when you did your calcs did you check for volt drop, and resistance of the cable .as then size you mention seams a little small for that size of supply over that length of runJust easier to terminate
I've done a quick rough calculation and come up with a 120mm four core SWA giving a VD of 4.4V and a Zs of 0.5ohm, which I would say is probably cutting it quite close on the voltage drop if working to the 3% rule for the lighting circuits in the house
Thanks for the feedbackIs that at 100A out of interest?
Reply to Installing 3 Phase supply to new 5/6 Bed house in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net