Thanks for the feedback
i think the property would only need a 60amp 3 phase supply

Make your mind up, you started at 100, then 80 now you're saying 60. These are all suspiciously round numbers for a calculated demand and look more like you are guessing at the numbers.

Have you done any calculation of the design load for this circuit?
 
I believe circuit breakers are designed at 1.45 times ib , assuming some of these loads are very short duration ,unless some people spend an awful long time in the shower?

Eh? Relying on the operating characteristics of downstream circuit breakers to design a submain in this way is bad practise and far from sensible.
 
I believe circuit breakers are designed at 1.45 times ib , assuming some of these loads are very short duration ,unless some people spend an awful long time in the shower?


With all due respect here Martin, regarding this comment of accepting overload in design just because you hope no one has a long shower -- well I'm rather worried by that.

@ The OP - before we go any further with help here, can you show your calcs for estimating the house demand and also your calcs for your supply SWA, it seems you plucking numbers and figures out of thin air here and changing them to suit the response.
 
Last edited by a moderator:
Sorry folks
Maybe I have been to long with Pierre today, I have no calculations to back any of my posts up ,but the point I am trying to get across is that most large houses are supplied with a single phase 100a , which seems to be adequate for their needs , adding a couple of bedrooms should not add a ridiculous amount of maximum demand, divide this up over three phases and you should not exceed much more than 40a per phase on balanced ,load this is based on diversity to calculate VD ,and not the CCC of the cable
PS I Am going to bed now before I suffer the same fate as Paul the magpie
 
Sorry folks
Maybe I have been to long with Pierre today, I have no calculations to back any of my posts up ,but the point I am trying to get across is that most large houses are supplied with a single phase 100a , which seems to be adequate for their needs , adding a couple of bedrooms should not add a ridiculous amount of maximum demand, divide this up over three phases and you should not exceed much more than 40a per phase on balanced ,load this is based on diversity to calculate VD ,and not the CCC of the cable
PS I Am going to bed now before I suffer the same fate as Paul the magpie


Haha the PS bit made me chuckle
 
Sorry folks
Maybe I have been to long with Pierre today, I have no calculations to back any of my posts up ,but the point I am trying to get across is that most large houses are supplied with a single phase 100a , which seems to be adequate for their needs , adding a couple of bedrooms should not add a ridiculous amount of maximum demand, divide this up over three phases and you should not exceed much more than 40a per phase on balanced ,load this is based on diversity to calculate VD ,and not the CCC of the cable
PS I Am going to bed now before I suffer the same fate as Paul the magpie

Your added problem with regards to the cable size is that it will have to be based on the neutral current unless you can perfectly balance the phases. So you might end up going up two sizes anyway.
 
A high spec 5/6 bed house (the sort of house than might be down a 100m drive) will often have a lot more appliances than typical.

I've worked recently on one such house, e.g. the kitchen has 2 built-in ovens, built-in warming drawer, built-in steamer, built-in microwave, 6-ring hob. The plant room has a couple of big water tanks with backup heaters in case the gas boiler fails. Every bedroom has an en-suite (though depending, the showers might not be electric). It needed a lot more than 100A.
 
Sorry folks
Maybe I have been to long with Pierre today, I have no calculations to back any of my posts up ,but the point I am trying to get across is that most large houses are supplied with a single phase 100a , which seems to be adequate for their needs , adding a couple of bedrooms should not add a ridiculous amount of maximum demand, divide this up over three phases and you should not exceed much more than 40a per phase on balanced ,load this is based on diversity to calculate VD ,and not the CCC of the cable
PS I Am going to bed now before I suffer the same fate as Paul the magpie


Sorry Martin that was my bad - I didn't segregate my post, its done now though, I should have multi-quoted :blush5:
 

Reply to Installing 3 Phase supply to new 5/6 Bed house in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
594
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
949

Similar threads

Given that a lot of EV's only charge from one phase when connected to a 3 phase chargepoint does the customer really need a 3 phase chargepoint...
Replies
1
Views
678
Just stick the 63amp fused connector before the Henley block , or Lucy block as you call it, and your all good, as for your 2nd point, , the...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top