Even so , will still probably house 2 adults ,4 kids at most
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Installing 3 Phase supply to new 5/6 Bed house in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Is that at 100A per phase out of interest?
That S.W.A. will probably weigh around ¾ of a tone. I hope he’s got some butch cable jacks and bouts of energy.:yes:
Thanks for the feedback
i think the property would only need a 60amp 3 phase supply
I would be basing my design load at no more than 40a per phase.
Even so , will still probably house 2 adults ,4 kids at most
I believe circuit breakers are designed at 1.45 times ib , assuming some of these loads are very short duration ,unless some people spend an awful long time in the shower?
I believe circuit breakers are designed at 1.45 times ib , assuming some of these loads are very short duration ,unless some people spend an awful long time in the shower?
I believe circuit breakers are designed at 1.45 times ib , assuming some of these loads are very short duration ,unless some people spend an awful long time in the shower?
Sorry folks
Maybe I have been to long with Pierre today, I have no calculations to back any of my posts up ,but the point I am trying to get across is that most large houses are supplied with a single phase 100a , which seems to be adequate for their needs , adding a couple of bedrooms should not add a ridiculous amount of maximum demand, divide this up over three phases and you should not exceed much more than 40a per phase on balanced ,load this is based on diversity to calculate VD ,and not the CCC of the cable
PS I Am going to bed now before I suffer the same fate as Paul the magpie
Sorry folks
Maybe I have been to long with Pierre today, I have no calculations to back any of my posts up ,but the point I am trying to get across is that most large houses are supplied with a single phase 100a , which seems to be adequate for their needs , adding a couple of bedrooms should not add a ridiculous amount of maximum demand, divide this up over three phases and you should not exceed much more than 40a per phase on balanced ,load this is based on diversity to calculate VD ,and not the CCC of the cable
PS I Am going to bed now before I suffer the same fate as Paul the magpie
Sorry folks
Maybe I have been to long with Pierre today, I have no calculations to back any of my posts up ,but the point I am trying to get across is that most large houses are supplied with a single phase 100a , which seems to be adequate for their needs , adding a couple of bedrooms should not add a ridiculous amount of maximum demand, divide this up over three phases and you should not exceed much more than 40a per phase on balanced ,load this is based on diversity to calculate VD ,and not the CCC of the cable
PS I Am going to bed now before I suffer the same fate as Paul the magpie