sorry if I come across as a git, but I don't mean to honest.

C'MON PETE, WHY BREAK THE HABIT OF A LIFETIME? :sleeping:
 
Don't know if it's me but your description of the readings you are posting are misleading, to help us/me help you, you need to be more explicit when describing your readings "I tested as 2 radials and got 0.00" don't mean a lot you have to admit, sorry if I come across as a git, but I don't mean to honest.

Sorry not a problem my fault. So the insulation resistance readings test at 500v

L-N = 500>megohms (reading fine)
N-E = 500> megohms (reading fine)
L-E = 0.00> megohms

Quickly split the ring circuit and tested as two radial circuits and on both radial legs I got the reading again of 0.00> megohms which i wasnt expecting. If there was a break in the cable i should be getting a reading on one radial circuit.
 
Yes its a new install.

Well assuming you are the one who installed it you would know if there are any hidden outlets with something still connected, in which case sounds like its time to split the circuit down half by half until you find the culprit. Keep us posted with your findings. Could well be a pinched live in metal back box
 
I assume there are no USB integrated sockets or surge protectors in circuit? If there are then it might be worth testing at 250V to see if the fault appears to clear.

If you are getting 0.00 MΩ it is often worth changing to low ohms and see if the result is a short or if the value can give an indication of the type of connection.
If you also get 0.0Ω on continuity you know it is a direct contact.

Because you are getting this reading on both side of the ring it sounds like either a cable manufacturing fault or a repeated installation error where someone else was unaware of the the cable location and has damaged it in all directions. however this seems unlikely and may just indicate a wiring error on some accessories.
 
It also may assist,to describe how you separated the RFC,how and where it was tested. It seems unfortunate that the same identical fault should appear on both halves.

If the fault is described accurately,it should take only one more splitting of the RFC,and the re-testing of the now disconnected six cable ends,to determine whether it is a fault,or a testing error.

Accurate terminology and result nomenclature,is vital. It is not "picky",to pull anyone up,on mistakes of this nature.

If you took your pregnant missus on holiday, to a foreign land,and asked regarding medical assistance,you would not be thrilled to find out it was 100 miles or 100 minutes or 100 pounds away...

With an accurate description of a circuit layout,together with test methods,and results,a fair guess can be attempted,at possible issues,and additional methods to apply.
 
Probably a daft suggestion, but sometimes the daft ones are the best ones - you've removed your temporary links at the board (sometimes installed line -> cpc to measure R1+R2 of other circuits) if you used them?
 
Probably a daft suggestion, but sometimes the daft ones are the best ones - you've removed your temporary links at the board (sometimes installed line -> cpc to measure R1+R2 of other circuits) if you used them?

The OP has stated its a ring final circuit, test links betwenn R1 & cpc would only be used on radial circuits.
 
The OP has stated its a ring final circuit, test links betwenn R1 & cpc would only be used on radial circuits.

Hence why I said "to measure R1+R2 of other circuits" - the scenario I had in mind:

OP puts temp link in to measure all his R1+R2's (new install, could be lots of circuits). Then does his rfc tests (end to end and R1+R2) and then terminates the cables back in the mcb etc. Then he comes along to test IR as a whole board (which is acceptable) forgetting he has a temp link, which would give him a dead short line->cpc.

I know it's a long shot, and very unlikely, but it's a valid suggestion in my mind still and it has cost me nothing to put it forward.
 
Did you have any look finding the fault? Did you try completely splitting the ring to every individual point and testing every single cable run? Have a good look at every point on the circuit, I had a similar fault once, turned out when one of the sockets was being pinned back into the backbox the socket pin caught on one of the live conductors and caused a nick! And it wasn't me before anyone says anything!!
 
Yes found the problem yesterday morning, it was a plaster board screw straight through the wire which the plasterer have carefully placed. Problem solved, thank you to all who gave useful advice.
 

Reply to Insulation resistance problem in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
494
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
973
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
907

Similar threads

Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...
Replies
2
Views
420
  • Question
That would depend on the instrument. On my old BM10 when you press & hold the button it just powers up the inverter circuits to generate the...
Replies
5
Views
373

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top