Insulation resistance test on length of SWA cable | on ElectriciansForums
Discuss Insulation resistance test on length of SWA cable in the Talk Electrician area at ElectriciansForums.net
T
Toneyz
Doing new supplies for a school new Shneider 3 phase & N MCCB panel board. 50mm 4 core SWA one end made off in the board earth fly lead from banjo to earth terminal. The other end gland made off in gland (fly lead not made off yet) 3 phases and neutral just hanging there. Done installation resistance test to earth at 500v got 10Mohms to earth on all phases run is about 50mtrs?
What is it connected into at the board that’s made off? Thinking you’re reading through equipment.
Either that, or the cables damaged somewhere
You mean INSULATION resistance test Mate surely
Did you try drying the exposed surface of the insulation between the bared ends of the cores and the gland? 10MΩ could just about be caused by condensation.
I think 'vgi' should read Vigi, Schneider's trade mark for their residual current add-on actuator.
Reply to Insulation resistance test on length of SWA cable in the Talk Electrician area at ElectriciansForums.net
Thanks, I was hoping someone could confirm whether it was odd or not. I've done a fair bit of insulation testing but only on a small number of...
I may have been mistaken regarding TT I will look into that, thank you for the valued reply, but in general I stick to my post, a good topic for...