Insulation resistance test readings. | on ElectriciansForums

Discuss Insulation resistance test readings. in the UK Electrical Forum area at ElectriciansForums.net

Jm1980

-
Joined
Oct 5, 2014
Messages
56
Reaction score
16
Location
Rochdale
Had an interesting one today, ring circuit blown the Mcb in a kitchen apparently a few times over last day or so. It has blown once when nothing was really in use in kitchen so kind of ruling out overload.
When turned up and turned it back on it held for maybe 5 minutes before blowing again…. Unplugged everything and tested IR which was down on L-N,L-E & N-E.
Rcd never tripped & also tests fine.

Quickly traced this down to one leg of the cable between the CU & socket outlet…. Readings all 0.01M ohm so thought maybe still something connected.
Switched the meter to continuity and got
L-N 6kohm
L-E 80k ohm
N-E 70k ohm

Tested the other side of the ring and all fine so powered this up with a 20A MCB now as cpd. This 'questionable leg left out of circuit.

Plugged items in individually, tried them and circuit held fine.
Had another hour looking at the cable leg id left out to see if I’d missed anything plugged in or neons ect and couldn't see anything. Powred up half of circuit held all this time with equipment plugged in.

Anyone had similar readings as they look like something connected to me but the fact the mcb has held & appliances seem ok means cable damage can’t be ruled out on this questionable leg?

Cheers.
 
Last edited:

Reply to Insulation resistance test readings. in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

The instructions tell you to test the insulation and you already know from the result of the previous test that the L and N are not insulated from...
Replies
4
Views
478
davesparks
D
If the main switch is on when testing global IR then the neutral and earth will likely give a very low reading. Not that anyone would...
Replies
10
Views
532
loz2754
L

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top