Hi all ran a ring circuit for someone about 6 months ago and when I carried out the insulation test my results were around 250 m ohms for l-n and slightly lower for l-e, anyway didn't think anything of it as we had just plastered all the rooms where the ring circuit went.

Returned to the same job today and thought I'd just check it while I was there, anyway instead of the results rising which I would have hoped they have actually dropped to around 150 ohms still well within the requirements but it's dropped never the less.

I investigated further and split the ring circuit at the half way point and tested each way, in doing so I got results which were higher on both legs separately then when they were together.

Connected everything back up and re tested from the consumer unit and the results had lowered to 150 ohms again,


Has anyone come across this before? I don't think it can still be damp that is cause the results to decress , could it be a problem with one of the socket fronts that is causing the lowering reading?

thanks for the help in advance

Chris
 
Had you tried keeping the test going and see if it rose steadily? in this case I would have thought it was damp in the fittings.

Someone could have poured juice over a socket the day before.
You may have had stronger batteries in your tester when you were testing today.
 
Don't you listen to all those cynical,angry electricians :rolleyes2: If you have the time and patience to check and re-check those readings,fair play to you.I have done this for years with things like Ra readings,call it research,interest or devilment,but it is these things that build up your experience and keep you keen.Remember not to let BS7671 spoil any joy to be had from the job.
 

Reply to Insulation resistance testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
285
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
786
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
804

Similar threads

Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...
Replies
2
Views
332
Thanks, I was hoping someone could confirm whether it was odd or not. I've done a fair bit of insulation testing but only on a small number of...
Replies
4
Views
280

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top