Unless you're not on the ground...At EHV you don't have to worry about touching a live conductor. You would be dead well before you touched anything.
Interesting stuff,
I thought HV power distribution was delta, so no neutral (star point)
I have no basis for this, other than my own conclusion from looking at 3 wire overhead lines, going to what i presumed were delta to star transformers to step voltage down to 230v (415v) and provide a neutral / earth for consumers??
Nope, the same, I have had little to do with transmission stuff in a practical sense.I wouldn't do that job for any money! I wouldn't climb the pylons either. I'm happy when I'm just climbing about all over the transformers ?
LV networks are always solidly earthed and may be TT TNS or TNC-S.Does the grounding at the HV-MV substation play any role? I've heard that MV systems in the UK are resistance or peterson coil earthed. Is this true?
Protection as in relays or on TX protection like Bucholz, PRV's WTI/OTIs etc?Only been involved in the protection side of it, so far far away...
Relay, at one (two) time I worked for a couple of protection equipment manufacturers and their associated consultants.Protection as in relays or on TX protection like Bucholz, PRV's WTI/OTIs etc?
On the relays eh? So you're on the high paid jobs and the nice warm/ air con switchrooms tapping keys on a laptop while us real workers are crawling all over the transformers getting soaked in transformer oil with the rain running down the necks of our overalls ? Okay, we do spend time in the switchrooms too, doing the maintenance/timing tests etc. on the breakers. We normally use our own guys for protection or if we are fully booked then we call in guys from Oberon Engineering.
I had wondered about this with the small (0.5MVA) substation that feeds our stuff. The map of buried cables shows it fed from an 11kV 95mm 3-core aluminium cable.The main distribution voltage is 11kV although other voltages are used. The 11kV network can be solidly earthed or resistance earthed through liquid or dry resistors.
Not locally, no.I had wondered about this with the small (0.5MVA) substation that feeds our stuff. The map of buried cables shows it fed from an 11kV 95mm 3-core aluminium cable.
I had always assumed it would be a simple delta-star transformer with just the star point of the LV (230V) side earthed and the HV side earthed at the source end, but is it likely to have an HV side earthing transformer as well?
I mean each rod was 10-15 ohms.However, it is an area of good soil conductivity, as I got around 10-15 ohms for a couple ord 2m x 16mm rods driven in to the forever damp clay soil there