i always do an IR test on all the circuits before removing a CU to change it, any suspect readings and the changeover stops.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss intermittant overall rcd fault in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
My money is on a low IR N - E fault on your ring final.
The more you load it (eg cooker/ microwave) the higher the current
will be that's bypassing the Rcd (parallel conductors) - It may only
be a tiny amount flowing via the cpc but it only has to be 20/25 mA
and...trip
The likes of the TV etc probably won't draw enough to do it.
That's my bet anyway - looks like you might be spending the day
splitting the ring[/QUO
yeah agree with that it's almost always N-E, I've had 3 or 4 that sound similar
I've 'solved' a similar tripping problem twice before when happening upon L-N polarity reversals in socket outlets.