Internal or external isolation switch for aircon | on ElectriciansForums
Guest viewing is limited
  • Thread starter Deleted member 112675
  • Start date
  • Replies 35
  • Views 5K
  • Tags
    None

Discuss Internal or external isolation switch for aircon in the UK Electrical Forum area at ElectriciansForums.net

D

Deleted member 112675

Hello all.

Split aircon with an external and internal unit both needing power. It seems the external takes the power and then there is an onward (power and control) connection from the external to the internal.

My question is, is it ok to site the isolator inside close to the internal unit? That would mean if an issue occured with the outdoor unit, I would need to run inside through an external door to get to the switch. But if it is placed outdoors then the same issue occurs in reverse if the indoor unit starts smoking or something....

I'm ok either way but what would the regs say ?
 
Main supply to outside, then a second isolator at the indoor unit, just for that unit.
That applied to the hundreds I've seen and or worked on in commercial buildings.
Thanks a lot for your reply but that would mean connecting the manufacturer supplied cable (designed to connect outdoor to indoor unit) to an indoor isolating switch. It doesn't feel like that would be the manufacturer intention ?
 
Thanks a lot for your reply but that would mean connecting the manufacturer supplied cable (designed to connect outdoor to indoor unit) to an indoor isolating switch. It doesn't feel like that would be the manufacturer intention ?
If you really need two points of isolation then you could use two isolators on the supply to the aircon one inside and one outside
 
I can’t understand why you would need an extra isolator for the indoor unit when the outdoor isolator will isolate both the indoor and outdoor units.
Agreed, and if you are inside and need to isolate, presumably the MCB is inside (I means as quick solution)
 
So the consensus seems to be isolator outside at a minimum. That would tally with how I think its done in the US and other countries where aircon is common.

No doubt many of the friendly and helpful electricians on this forum will be installing more and more split aircon in the UK (esp in the South) and maybe the next edition of the wiring regs will make what to do even clearer.

I'm (obvisouly) not a spark but the last time I read my copy of the 18th, I thought isolation switches were not just to be used for maintenance but to be used in an emergency. The aircon user having to run outside to turn off an indoor unit or fiddle with a CU doesn't seem great.
 
Thanks a lot for your reply but that would mean connecting the manufacturer supplied cable (designed to connect outdoor to indoor unit) to an indoor isolating switch. It doesn't feel like that would be the manufacturer intention ?

What exactly has the manufacturer specified in their instructions?

To date, every air con installation I've been involved with has had supply to rotary isolator at external unit. This provision is made at the behest of air conditioning engineers.
 
What exactly has the manufacturer specified in their instructions?

To date, every air con installation I've been involved with has had supply to rotary isolator at external unit. This provision is made at the behest of air conditioning engineers.

As you say supply to the external unit. The manufacturer supplied 4 (or 5 ) core cable then runs from the external unit through the wall and supplies power (and control) to the internal unit.

That obviously means the internal unit can't be quickly isolated should it prove necessary.
 
As you say supply to the external unit. The manufacturer supplied 4 (or 5 ) core cable then runs from the external unit through the wall and supplies power (and control) to the internal unit.

That obviously means the internal unit can't be quickly isolated should it prove necessary.

What means of isolation have the manufacturer stipulated in their instructions?
 
It implies to my laymen's eyes, it needs to be protected by a 16A RCBO of the given spec (disconnect if leak of 30mA or more in 0.1 sec or less). There is no mention of a switch so you're probably right.

Brings me on to my next question which maybe I should create another thread for but as far as I know this can be spurred off an existing 2.5mm ringmain that isn't overly used. The product spec says maximum running current 9 amps. Nowhere does it mention it needs a dedicated circuit.

Thinking about it, if the spur was a fused spur at 16A and the entire existing circuit was protected at the CU with either RCBO (rated well above 16A) or global RCD, that would satisify the requirements?
 

Reply to Internal or external isolation switch for aircon in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

Hello Brianmoooore, Thanks for yor reply - Sorry that I did not see your message until today - the Forum replies notification emails about your...
Replies
7
Views
569
  • Question
"A catalogue of errors" would be the appropriate phrase here and I agree with Avo and James that HSE need to be involved rather than this forum...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top