Ip44 230v zone 1?! | on ElectriciansForums

Discuss Ip44 230v zone 1?! in the Lighting Forum area at ElectriciansForums.net

in any zone RCD protection is required. not just zone 1. IP44 is suitable for installation in zones 1 and 2.
 
Minimum requirements for zones 1 and 2 is IPX4. The presence of additional rcd protection does not affect this rating.
 
Zones 1 & 2 the equipment must be IPX4 so IP44 is fine unless you are using water jets where IPX5 is required.
 
Minimum requirements for zones 1 and 2 is IPX4. The presence of additional rcd protection does not affect this rating.
agreed, though any circuit within or passing through the zones required RCD protection, irrespective of it's IP rating and suitability for installation within zones. manufacturers need to get a grip and supply instructions that are compliant and not confusing.
 
agreed, though any circuit within or passing through the zones required RCD protection, irrespective of it's IP rating and suitability for installation within zones. manufacturers need to get a grip and supply instructions that are compliant and not confusing.
I agree but existing installations may not have additional rcd protection however you can still replace a like for like/similar light fitting as you are not altering the circuit.
 
in any zone RCD protection is required. not just zone 1. IP44 is suitable for installation in zones 1 and 2.
The zones are from the finished floor level what if you shower try is not on the finished floor level what if its raised up 6inches would you measure the zone from the tray or the bathroom floor
 
showers spray the water jets donwards. something to do with gravity.they ain't spraying up to the light unless it's a cat having a shower, then all bets are off. them pesky felines pi$$ anywhere.
 
The height of zone 1 and zone 2 are limited either by the horizontal plane corresponding to the highest fixed shower head or water outlet, or the horizontal plane lying 2.25 m above the finished floor level, whichever is higher.
So it is the finished floor level you go off.
 
The zones are from the finished floor level what if you shower try is not on the finished floor level what if its raised up 6inches would you measure the zone from the tray or the bathroom floor
floor. that's what it sez in the magic picture book, commonly called on site guide.
;
 
The height of zone 1 and zone 2 are limited either by the horizontal plane corresponding to the highest fixed shower head or water outlet, or the horizontal plane lying 2.25 m above the finished floor level, whichever is higher.
last time i experienced a horizontal plane,I was landing it. makes a right mess if you hit the runway at 45 degrees.
 

Reply to Ip44 230v zone 1?! in the Lighting Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Unfortunately I don't think you will get an "off the shelf" diagram for the system you are trying to do The Wiser system is very adaptable but it...
Replies
1
Views
489
Thank you..... & did have all the fan isolator/ fuse in same plate (click) so quinetic wouldn't worked on this occasion
Replies
12
Views
768

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top