andyelectric
I recently changed my consumer unit at home. Since my old wylex rewireable had all cables entering through the top I came through the top of the new unit via knockouts. I then proceeded to fanny around making the top IP4X. I used trunking, but reading up I notice others have various ingenious methods.
Next time, I'll come in through the back via battening or chasing wires. But I was thinking surely the cu manufacturers would not be supplying boxes that have non compliant knockouts. So, noting that in the regs a minimum of IPXXD would ensure compliance I opened up my unit and started measuring.
As the neutral and earth bars are shielded from the knockout, and the tops of the din mounted components far enogh down inside the box the consumer unit would indeed be IPXXD without worrying about tidying up the knockouts.(only just)
Are consumer units generally IPXXD without further work, and is it necessary to upgrade the ones that are to IP4X via what can be pretty makeshift arrangements.