hi guys,

really hope you can enlighten me, i just did a periodic, and was going to connect L-N then test to earth for the insulation resistance test, client agreed to the Lim, i was getting no readings so i reverted back to standard 1 circuit at a time, L-N, L-E, N-E.

i started with the cooker as its the most simplistic circuit, L-N & L-E >500 but N-E no reading?

then when i came to do the ring final i got no readings at all??? yet they've never had any tripping problems.

i've only recently passed my 2391 which always explains what readings you should get but doesn't go into so much detail about iffy readings, and what causes them etc... hope someone can help me, and i'm sure this will be just 1 of many post from now on:D

ps. is there a website with a list of common testing problems with possible causes/solutions? that would be fantasic.
 
hi johnboy, must admit i didn't remove the cpc and neutral cables from cu, but will try that, the system is a TN-S, earthed to the supply sheathing.
 
even in a TNS sstem, the earth and neutral will be linked at the supply transformer. in newer transformer installs ive seen, the star point of a transformer is connected to a busbar, which all of the main bonding of the transformer is connected to. this is then connected to an earth mat which is laid underneath the transformer, during the groundworks.

Ive never seen an old transformer that supplies domestic properties though!
 
If this is domestic
The main isolator would be in the off position
The installation neutral would be isolated from the network
The earth -neutral wont be reading unless there is a fault or

Were the readings taken with an Rcd/Rcbo in circuit
Especially ones with a tail earth monitor,you will get false readings unless you dis connect those

Was the cpc continuity tests done before the insulaton resistance
 
hi des, the cpc continuity was done and was fine, but the circuit was rcd protected, i know this is probably a stupid question but wouldn't the rcd give me a false(low) reading as apposed to 3 zero readings?
 
Just put paint pot back down :)

The Rcd or Rcbo may give a virtual zero reading neutral - earth because the reading being in thosands or millions of ohms would be indistinguishable from a low reading on the insulation tester

If there is a load or neon or simillar in circuit the line -cpc may also give that same reading

Another test making sure nothing will be influencing the result would be my way forward
 
good thing my missus didn't see that post, she'd have the roller in my hand so fast my head would spin.

cheers for the advice, i'll go through the tests again, making sure i haven't missed anything, it'll all come good with experience i suppose.
 
Risteard

I am well aware of the scale and value

Half a meghom = 500 thousand ohms

When we use an insulation tester,the readings obtained when getting a low value in perhaps thousands of ohms,when the tester is trying to measure in millions of ohms.the lower values whether dead shorts or low resistance cant be distinguished between that dead short or low insulation resistance
 
Last edited:

Reply to IR readings problem? Confused newbie in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
279
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
776
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
787

Similar threads

  • Question
They ought to be able to check for the voltage going completely off using one MCB off at a time to confirm that. That would be my assumption...
Replies
9
Views
853
  • Question
It is actually specified in BS7671 that the cpcs must be connected to all other sources of earth.
Replies
9
Views
759

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top