hi was just wondering if some one could clear this up for my i keep seeing on the open forum that people do a ir test between l+n to cpc i get shown at college to do the ir between l to e and n to e and l to n so why is it that i keep seeing people say about doing a ir by connecting live and neutral then testing from the connected live and neutral to earth wont this defeat the object of doing the ir test as it wont test between l and n as there connected together,

here is a link to the last one i saw
http://www.electriciansforums.net/i...allations/73680-ir-method-2-a.html#post732492
 
Funny that, we are going through T & I at college at the moment and this method hasn't been discussed.

To short L and N only seems practical if you've already proved that the IR values between all conductors are acceptable, and no dead-short exists between L and N.

I assume this method is used when attempting to determine if there is a path to earth via one of the live conductors, in the event of nuisance tripping of an RCD, for example. It makes sense to short L and N in this case.
 
I thought testing between L+N to CPC was so that any sensitive equipment that hasn't been or can't be removed from the circuit does not get damaged. ie if you put 500v between L and N it would fry any sensitive equipment. I could be wrong as i'm a trainee too..
 
So how will that stop sensitive equipment from being damaged it will still send 500 volts down it and also if it does stop equipment getting damaged then why dont we always do the test this way
 
Even at 250, testing between L and N you'll not get an answer in Mohms. You won't even get an ohm most times, an example is those plug in air fresheners. They usually give you 0.57ish
 

Reply to IR Test in the Electrical Course Trainees Only area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
279
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
776
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
787

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top