hi guys have u seen this before ( probably) lol

i get a reading of 0.00 on my r1 + r2 test

test is on a new cu in garage usual link in from line to earth fluke set to insulation it reads 0.00 ??

also when doing an end to end test line & neutral ok readings earth gives >2000 open circuit..why? practising testing lol.:D
 
If you are linking out at the board and using the IR test then you will have a reading of 0.00! you need the continuity test setting to measure your r1+r2!
 
you need the fluke set to ohms for your r1+r2. insulation resistance is a completly different test. not sure about fluke but the new megger 1552 ive just brought comes with a dvd which will take you through all the settings on your meter.
 
You've clearly got slightly confused between the dead tests. You'll need to grasp a better understanding soon because applying 250V/500V (or possibly even 1kV) on an R1&R2 test is actually quite dangerous.
Have you purchased any books for guidance?


oh and it's R1&R2, not r1&r2. :)
 
you need the fluke set to ohms for your r1+r2. insulation resistance is a completly different test. not sure about fluke but the new megger 1552 ive just brought comes with a dvd which will take you through all the settings on your meter.

jam2020

Sorry to jump on this post.

I bought a megger 1553 (so basically the same as yours) - just wondered what is the dvd you got with it called as I would have I would have possibly had one.

Got a couple of discs with it but pretty sure it aint got any dvd's with it.
 
it was just a megger dvd that came with it.ive since found it on youtube so check it out there.dont think there is much difference regards controls of the 2 meggers so should apply,
 
i've got the 1552. it's as easy to use as a multimeter and 10 times more use. battery life is cak though
 

Reply to ir testing reading 0.00 on ring main and lighting circuit. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
353
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
320
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
368

Similar threads

  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
5K
In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top