Hi All

With the introduction of electronics into socket outlets and other devices. IR testing has become very laborious, I am only talking about EICRs, I spend more time looking for possible causes for low readings than anything else.
From another forum I gathered there was talk of doing away with the IR test.
What are your thoughts on this.
 
My take on it is it is an ingenious method of assaying the state of cables in an installation. I eschew the global LN to E as I feel it is a very incomplete test and like to get into the installation more and know exactly what is going on. I am sure that is heresy but that is just me, curious and really want to be sure that when I say a circuit is safe to keep in use I know it is. I know there are instances where that is just not practical but still I will gravitate toward L-N L-E N-E where I can and yes I keep the earth in the earth bus bar!
 
I only ever do IR L-L and L-N on initial verification. It is too disruptive and unnecessary for an existing install.

As far as testing periodically, For the breakdown to occur between those it would require 2 faults, which if there is a path between them, almost certainly there is a path to earth which you can pick up on LN-E test. That's would guide you to investigate further.

Cliffed. That's is soo true lol. All these 299 readings we see, which you know haven't even been tested due to what would of had to have been disconnected to achieve that.
 
I only ever do IR L-L and L-N on initial verification. It is too disruptive and unnecessary for an existing install.

As far as testing periodically, For the breakdown to occur between those it would require 2 faults, which if there is a path between them, almost certainly there is a path to earth which you can pick up on LN-E test. That's would guide you to investigate further.

Cliffed. That's is soo true lol. All these 299 readings we see, which you know haven't even been tested due to what would of had to have been disconnected to achieve that.
I'm going to take that sage advice, as I like the sound of it.
 
My take on it is it is an ingenious method of assaying the state of cables in an installation. I eschew the global LN to E as I feel it is a very incomplete test and like to get into the installation more and know exactly what is going on. I am sure that is heresy but that is just me, curious and really want to be sure that when I say a circuit is safe to keep in use I know it is. I know there are instances where that is just not practical but still I will gravitate toward L-N L-E N-E where I can and yes I keep the earth in the earth bus bar!
Great to see the English language used so eloquently. Your line , “I know there are instances where that is just not practical” sort of puts it back to having to use L&N to E method, which increasingly is the case.
 
In the 'old days' before the widespread use of switchmode power supplies (chargers, PC power supplies, LED drivers etc) you could do an IR test and if you did a leakage clamp test around the supply live and neutral the results of both tests would tally.

Nowadays an global IR test gives little or no indication of leakage (functional or fault).

I'd only see the value of an IR test if you're fault finding or as a dead test on a new installation or circuit.
 
In the 'old days' before the widespread use of switchmode power supplies (chargers, PC power supplies, LED drivers etc) you could do an IR test and if you did a leakage clamp test around the supply live and neutral the results of both tests would tally.

Nowadays an global IR test gives little or no indication of leakage (functional or fault).

I'd only see the value of an IR test if you're fault finding or as a dead test on a new installation or circuit.

I am coming around to that way of thinking as someone mentioned you often see 299MÎŹ on a EICR and you just know it's false.
 
Nowadays with TPN boards filled with RCBOs IR testing is becoming a right headache. Disconnecting individually from each RCBO rather than a global test
 

Reply to IR Testing what is your take on it? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
382
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
963
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...
Replies
2
Views
351
I was at the other end of the results spectrum today. As I was driving home I had a call from my "Mrs Richards from Fawlty Towers" lady, very deaf...
2
Replies
20
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top