Ir tests | Page 3 | on ElectriciansForums
Discuss Ir tests in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
A value of 725 Mohms is well above the maximum that some testers read to (300Mohm) so that result is absolutely fine. If you were testing a new install and got 75 Mohms then I may be slightly concerned.
14 years is plenty of time to have got to 750 Mohm even if it did not start at that.
Absolutely. Don't worry about it Rob, you will see plenty lower on newer installs. :)
You're talking about 725,000,000 ohms - have you divided that into 230 volts to see what current leakage you're going to get?? - 0.0000003 Amps, I think.......shocking.:teeth_smile:
Reply to Ir tests in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Having some issues with my companys fluke 1662/1663 tester. Zeroing 2 leads for continuity test we get the value 0.08 which is expected. The issue...
I was at the other end of the results spectrum today. As I was driving home I had a call from my "Mrs Richards from Fawlty Towers" lady, very deaf...