Location
Liverpool
The electrician that installed my cooker circuit put in 10mm cable with a 32a fuse, a 45a cooker switch and 10mm cable to the backplate for behind the cooker. He put this size in as I didn't know what size cooker I was going to be getting.

I ended up getting a 7.4kw range cooker and the electrician has connected it with 4mm heat resistant cable instead from the cooker to the back plate, instead of 6mm. Is this okay, and is it okay with the 10mm cable and 32a fuse?

Thanks
 
The electrician that installed my cooker circuit put in 10mm cable with a 32a fuse, a 45a cooker switch and 10mm cable to the backplate for behind the cooker. He put this size in as I didn't know what size cooker I was going to be getting.

I ended up getting a 7.4kw range cooker and the electrician has connected it with 4mm heat resistant cable instead from the cooker to the back plate, instead of 6mm. Is this okay, and is it okay with the 10mm cable and 32a fuse?

Thanks
At least he used heat-resistant cable, most just use twin and earth.
 
Nothing wrong with T&E for the final connection to a cooker, This is fully compliant with BS7671
Where manufactures say to use heat-resistant flex, then using T&E wouldn't strictly be compliant with BS7671.
 
I'm yet to see T&E showing signs of deterioration behind an oven, but it's not the ideal cable for pushing back behind an appliance. Flex is inclined to drop easily behind a kitchen unit and naturally forms itself into position.
Loop of string around the cable, down the back to the space underneath and out the vent that should have been cut in the top of the kickboard. Gently pull on the string as you push the oven back into place.
 

Reply to Is 4mm heat resistant cable okay for 7.5kw range cooker? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
952
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Check the clearance between the back panel and/or terminal cover that you've removed. Look for small burn marks.
Replies
3
Views
499
  • Question
Obviously not a building/DIY forum so will keep it short but yes - we've taken all the floors up. Several joists in the bathroom need doing as...
Replies
8
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top