Hi Guys,

I've just been looking at a job that has been installed by another company.
One thing I've noticed are the feeds to 2 BMS / Plant panels. They have run in 2 x 150mm 4C and doubled up on the main switch in both panels. No separate CPC has been installed and the banjos aren't earthed either.
If this had been myself I'd have run in a separate CPC and bonded the Banjos.
Thoughts please is this to regs or does it need a separate CPC ?
 

Attachments

  • [ElectriciansForums.net] Is a separate CPC required ?
    20221021_130035.jpg
    284.7 KB · Views: 51
  • [ElectriciansForums.net] Is a separate CPC required ?
    20221021_130030.jpg
    395.6 KB · Views: 37
It is unlikely to need a seperate CPC, you need to do the calculation to confirm that though, it is impossible to tell from looking at it. The armour of SWA, especially with 2 in parallel is likely to be suitable as the CPC.

The connection to the banjo doesn't look too good however, they should have at least cleaned the paint off the metal where the bolt connects to it.
What is on the outside of the enclosure? Is the gland and banjo fitted to clean metal on that side?
 
Is the wire armour earthed the other end?
Might they have used the adiabatic equation (as the armour of 150 sq mm 4c SWA is only 73 sq mm equivalent copper)?
Is the body of the cabinet being used?
What are the earthing requirements of the load?
 
It is unlikely to need a seperate CPC, you need to do the calculation to confirm that though, it is impossible to tell from looking at it. The armour of SWA, especially with 2 in parallel is likely to be suitable as the CPC.

The connection to the banjo doesn't look too good however, they should have at least cleaned the paint off the metal where the bolt connects to it.
What is on the outside of the enclosure? Is the gland and banjo fitted to clean metal on that side?

Hi, the outside is the same as the inside, fully painted. They've just drilled the plate and bolted it down.
 
Is the wire armour earthed the other end?
Might they have used the adiabatic equation (as the armour of 150 sq mm 4c SWA is only 73 sq mm equivalent copper)?
Is the body of the cabinet being used?
What are the earthing requirements of the load?

Not that I'm aware of.
The cabinet is being used as the earth for outgoing Services connected to din mounted earth terminals.
 

Reply to Is a separate CPC required ? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Electric hob/oven range was installed years ago, runs on 2 x B32 MCBs to 'House' (sub)consumer panel, runs to oven on 2 x T&E. Kitchen is being...
Replies
0
Views
210
The power company only brings in 3 wires which is 2 live and 1 neutral wire. It’s our responsibility to add the ground rod to bond the neutral...
Replies
3
Views
510
  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
1K
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2
Replies
45
Views
5K
  • Question
Hi James. I agree that is a method of extending the ring which I have seen many times. However in this instance, the electrician who wired the...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top