juice

-
Joined
Jun 8, 2016
Messages
13
Reaction score
1
Location
Wolverhampton
I've been asked to install a shower unit in a clients house and he only wants me to change the shower itself. The consumer unit has BS3036 rewireable fuses and no RCD protecting any of the circuits, including the existing shower circuit. He has already bought the new shower and only wants me to change the shower unit so costs can be kept to a minimum.

Obviously as the shower is in a bathroom it must be backed by an RCD. Can the customer choose to not have an RCD put in and I put this down as a departure from BS7671?

Personally I want to put an RCD in as this is clearly the safest option to protect against electric shock in the bathroom, but who is it that decides the level of protection to be put in on an electrical installation? Cost is always an issue and can I insist that an RCD must go in or the work can't be done or is this at the customer's discretion?
 
Thank you for all your posts. Electricians forum is truly a brilliant resource for electricians facing the challenges of preventing harm coming to persons, livestock or property. Customers will most likely never appreciate the effort we go to ensure no harm comes to them or their family.

I've had chance to do a few more calculations and because the shower circuit is wired in 6mm2 and is protected by a BS 3036 fuse I cannot do a like for like swap. Due to the BS3036 fuse I must apply the Cf correction factor and this means the circuit must now be wired in 10mm2 cable if I want to keep the BS3036 fuse as the protective device.

To continue using the 6mm2 cable and prevent the need for a rewire of the shower circuit the other option is to change the protective device, which to me seems like the better option as it allows me to introduce an RCD. Now all I need to do is explain all this to the customer and check for any thermal insulation that could be present, which could also force a rewire to 10mm2.

Then I will just have to mitigate the costs as best I can for them. Unfortunately just like a car electricity has to be safe to use.
 
OP, you don't seem to be convinced by your peers here, i.e. to tell your customer you are not installing new shower without the installation of RCD?
There's minor discussion about other issues, but the recurring advice to you, is only install with RCD. If that's not to your customers pocket, let them find someone else.
 
Gents

In relation to an addition or alteration to existing electrical installations.

this thread goes to the heart of the tension between professionals and the domestic consumer which get faced everyday. Part P does, however, still direct us to designing and installing in accordance with BS7671.

Then we we get the bit which says the building should be no more unsatisfactory .... then when the building work was started.

Then we are directed to do any new work according to BS 7671 and we must check the existing installation a) rating and condition for new loads (does not say anything about like for like loads) b) Adequate protective measures are used c) Earthing etc satisfactory.

Then we are given the list of notifiable work, shower room for instance. This bit is important to this discussion, I suggest, as minor additions and alterations are notifiable in this case.

A simple swap, like for like model and rating of shower unit, would ordinarily pass the no more unsatisfactory test, as long as b and c above being satisfied.

Which leads us to BS 7671, if you agree with me so far. Where I suggest if we touch this particular circuit we adopt wiring regs and add an RCD. 701.411.3.6. Uses the word shall, not maybe, might, is optional etc.

cheers
 
As far as I am aware, there is no requirement to notify when replacing equipment, irrespective of whether the equipment is in a special location.

As for the OP's query, it is up to the person conducting the work to comply with the requirements of BS7671.
In this particular instance there is no requirement to provide RCD protection, as the work is replacing equipment.
 
As far as I am aware, there is no requirement to notify when replacing equipment, irrespective of whether the equipment is in a special location.

As for the OP's query, it is up to the person conducting the work to comply with the requirements of BS7671.
In this particular instance there is no requirement to provide RCD protection, as the work is replacing equipment.

But in this instance the equipment been installed comes with a manual and it will say in there that an RCD MUST be installed. No getting around it.
 
And consider the manufacturers installation instructions, which will advise RCD installation. We can always live in past, and install equipment connected to bare wires circa Edwardian times. But safety moves on.
 
It is quite possible that the manufacturer's instructions do specify RCD protection be provided.
Unfortunately, without knowledge of either the manufacturer or their instructions, I am unwilling to offer an opinion as to what such instructions do or do not require.
 

Reply to is it up to the customer what protective device is in his installation? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I'm begining to think like this now, I very rarely work for builders anymore but the couple that I still do work for are the worst payers out of...
    • Like
    • Agree
Replies
8
Views
681
I opened up the CU again and the round junction box above and what I found was the blue and brown wires coming in from the wall just above the 15a...
2 3
Replies
33
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top