1.3 no distributer earth connection between service cable and MET.
1.4 minimum CSA of meter tails.
1.6 isolator enclosure is not made from non combustible material.
what would you regard as error ? is it the wording you disagree with or the content
 
what would you regard as error ? is it the wording you disagree with or the content
Lack of a connection between the supply cable and the MET would be a TT earthing system and would not warrant a code.
There is no minimum CSA for tails in BS7671.
The requirement for non-combustible enclosure only applies to the consumer’s installation, so no code if the isolator is the Distributer’s equipment and at most would warrant a code C3 if the isolator is the Consumer’s.

Thermal damage has nothing to do with the requirement to use non-combustible material for the enclosure.
 
I’ve got the book.
They have also deemed pvc cables concealed in walls a C2 without additional protection via 30mA rcd, mechanical protection etc.
I’ve got the 17th edition version 1 book also given to us in a tool box talk ,where in that version cables concealed in walls etc ,is given what I would say as the industry collective opinion of a C3.
Don’t know if they have changed their minds or it’s a mistake in the publication?

It’s decent but as the inspector the codes are yours to put down and no one else’s in my opinion.
There’s loads of codes in the book I feel are not what I would code.
 
Oh dear! Cables not protected by an rcd in a wall a C3 but without mechanical protection a C2? (17th edition version) A bit of a cock up id say[ElectriciansForums.net] Is this the real bible eicr code breaker [ElectriciansForums.net] Is this the real bible eicr code breaker
 
^^ that's appalling

Lots of Napit members are going to be using this as the gospel truth
How can a cable not protected by an rcd be a C3 yet the likelihood of having mechanical protection is nil, but that is a c2 when both methods are acceptable to use ? they must be the same code if both are missing
 
Last edited:
How can a cable not protected by an rcd be a C3 yet the likelihood of having mechanical protection is nil, but that is a c2 when both methods are acceptable to use ? they must be the same code if both are missing

Inconsistent - must have be written by the guys who produce the regs...
 
Inconsistent - must have be written by the guys who produce the regs...
There’s quite a lot of input from various persons so I don’t think it’s been given a overall final say by a senior person/editor on the coding in general
 
This is rubbish.
There is no prohibition in BS7671 against running cables outside of prescribed zones or diagonally. They need to be protected by one of the listed methods.
I just hope people don’t start quoting this book as gospel and use it as the be all and end all of eicr coding
 

Reply to Is this the real bible eicr code breaker in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
848

Similar threads

Thanks for the reply littlespark. Yes the works have been carried out. Surely it is fraudulent because basically the document is Not...
Replies
2
Views
709
The challenge that you have with this is that you've no confirmed start point. Because you have a lack of an EICR you don't actually know what...
Replies
7
Views
586

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top