mackers
got a call from a customers mother could i call as the gas board electrician had condemend the electrics!
gas spark had left a cert stating defects after a quick check i agreed with his findings.
after speaking to the lady of the house it turns out she had an alarm fit beginning of the year2012 ,alarm engineer/ sparky
said your fuseboards is "DANGEROUS" i can change it if you want ÂŁ200
so fuseboard changed
100A MAIN SW & 7 MCB,s
NO CERT
8KW SHOWER WIRED IN 2.5 T&E
GAS NOT BONDED
WATER NOT BONDED
ALARM WIRED IN 1.0MM BACKED BY 20 A MCB
AND NOW ITS SAFE!!:banghead:
could go on but im bored as no amount of ranting is ever gonna rid our once great trade of these ,i won't use the word "cowboys" as the real name is "CROOKS"
GAINING MONEY BY DECEPTION