The Ghost

So there is no earth to the light fitting, well there is it's terminated in the black terminal box above it. However there is no connection of earth to the light. It's a JCC I think circa 10 years old or maybe less. Also the supply to the lamp holder is in singles from the termination box. There are around thirty of them throughout the flat. Now if you look up this light JCC it's Class II, although all metal. I'm thinking if the live came out of the lampholder and you were changing the lamp it could get interesting up that ladder! And the singles bugs me as well. But suggesting they should be changed with a C2 means 30 lamps at £xx could get pricey. Perhaps I am being too picky? What say you?
[ElectriciansForums.net] Just doing an EICR today and in a quandary...
 
Nay it's not double-insulated which is technically a problem but then ten years ago who would have worried about it? Yes I could easily take the view that its Class II but what worries me is it does not carry the logo of Class II. And anyway its patently clear on a common sense level it could present a danger there are 30 odd lamps in there and they do tend to go so someone is going to be up and down changing them regularly. The lampholder just floats around inside the housing giving rise to stress on the single insulated cables. But yeh maybe I am making something out of nothing, might C3 it just to cover my derriere. Will phone JCC tomorrow, I see TLC still sell them.
240v 50w GU10 Halogen Fire Rated Downlight - Chrome - https://www.tlc-direct.co.uk/Products/GUFRD50C.html?source=adwords&ad_position=1o9&ad_id=45425533757&placement=&kw=&network=g&matchtype=&ad_type=pla&product_id=GUFRD50C&product_partition_id=174054929347&test=finalurl_v2&gclid=EAIaIQobChMI6MDwjZqF2AIVh5PtCh3qzARhEAQYCSABEgJ-1PD_BwE
 
have to condemn all the fittings
Agreed which is quite an onerous task for the landlord at some cost. So I am thinking carefully on what to say about them to be fair to the landlord while not compromising on safety. If it was a couple in the bathroom, well maybe ok but in every room like 12 in the living room, they obviously liked downlighters.
 
Are you sure it's class 2? The manufacturers instructions say "Class 2 termination with earth provided" but I notice they also have the double square symbol which mayt be misleading. That could just mean the terminal box is class 2 and the rest of the fitting is class 1. Have you got a photo of inside the terminal block as it's possible the earth terminal is connected to the metal bracket that holds the terminal block to the light fitting?
 

Reply to Just doing an EICR today and in a quandary... in the UK Electrical Forum area at ElectriciansForums.net