Hi fellow 2391ers, seems c&g continue to love their ambiguity!! some questions in part 1 had me guessing and double guessing myself lol:sad3: what did you peeps work out the v drop to be?
 
I sat the exam last night too absolutely knackered now.
Volt drop question found a bit of a bugger i too came to 11.4v.
What did everyone put when inspecting the db with sight and touch? few marks i may have lost there!
 
For sight I put that the correct circuits were connected in the correct sequence in the main earthing terminal and the neutral terminal and that the MCB's and RCBO's were the correct size for the conductors leaving them. For touch I put that the earthing conductor was secure in its terminal and that the main switch operated properly. Can't remember the rest!
 
I sat the exam last night too absolutely knackered now.
Volt drop question found a bit of a bugger i too came to 11.4v.
What did everyone put when inspecting the db with sight and touch? few marks i may have lost there!
This is the bit that I struggled on, from memory I put:
Touch:Check all terminations into circuit breakers RCBOs earth and neutral bars are secure
Check buzz bar covers and barriers are secure and all in place
Check that switches and circuit breakers and RCBOs swith on and off cleanly
Sight: Check that the circuit breakers and RCBOs are suitable for the perspective fault current that could flow
Check the type and rating of circuit breakers and RCBOs are suitable for the size(csa) of the circuit conductors (cables) that are installed.
I think I ballsed this question up but the others seemed to go ok.
 
Last edited:
Don't you have to add a x1.2 correction factor to the volt drop formula to allow for the rise in temp when the circuit is under load?
I think the answer to Q4 was something along the lines of:-
1, Confirm installation/circuit complies with designer's intentions
2, Designed, Installed and Inspected & Tested to comply with BS7671
3, Not damaged so as to impair safety
Just seen it in some notes, not sure where it came from though as nothing in GN3.
Good luck to everyboby, only a couple of months to wait.
 
For touch i put

Connection of conductors - To check for any loose connections
Overheating of cables - Feel any cables that are overheating
Operation of protective devices - To check that all the protective devices were functioning correctly.

For sight

I put overheating and correct identification of condcutors.

Q4. If i remember correctly thats the on on inital verification fron GN3 i put.

1. All installed eletrical equipment and materials are of the correct type and comply to british standards.
2. All parts of the fixed installtion are correctly selected and erected.
3. No part of the fixed installation shall be visibly damaged or defective to impair safety.

Does anyone have the question papaer that they could post up?
good luck to everyone!!
 
Bugger I think the 1.2 factor is right for the voltage drop - got that completely wrong then!
Be interested to see the paper again

Not sure about 1.2 factor for volt drop, are you sure your not thinking of the X 0.8 tempreture correction factor for tabulated Zs to measured Zs .
 
Hi did the volt drop question give you a resistance at 20C or a table with the m/ohm/m values at 20c if so then needed correcting by 1.2 for the increase in temp due to load current ie say a 1.83 m/ohm/m =10mm conductor with another added in parallel ie line and neutral at 20c will need increasing by 1.2 as its a conductor bunched or a core in a multicore cable for thermoplastic (pvc) 70C max operating temp
table A.3 in GN3

m/ohm/m x 2 x MF x Ib X L/1000 = Vd
1.83 x 2 x 1.2 x Ib x L/1000
which will give same value as the mv/A/M tabulated value from the regs when using
mv/A/M x Ib X L/1000
or
R1+RN x 2 x Mf x Ib x L/1000

be good if someone could remember the question or somehow found the paper in there bag lol


this sounds like a question i had for the 2391 june 2010 and the only thing i forgot to include was the MF of 1.2 which i realised later when discussing it with forum members
good luck to you all
 
Hi did the volt drop question give you a resistance at 20C or a table with the m/ohm/m values at 20c if so then needed correcting by 1.2 for the increase in temp due to load current ie say a 1.83 m/ohm/m =10mm conductor with another added in parallel ie line and neutral at 20c will need increasing by 1.2 as its a conductor bunched or a core in a multicore cable for thermoplastic (pvc) 70C max operating temp
table A.3 in GN3

m/ohm/m x 2 x MF x Ib X L/1000 = Vd
1.83 x 2 x 1.2 x Ib x L/1000
which will give same value as the mv/A/M tabulated value from the regs when using
mv/A/M x Ib X L/1000
or
R1+RN x 2 x Mf x Ib x L/1000

be good if someone could remember the question or somehow found the paper in there bag lol


this sounds like a question i had for the 2391 june 2010 and the only thing i forgot to include was the MF of 1.2 which i realised later when discussing it with forum members
good luck to you all

Hi Brucelee, From memory the question said something like: the combined resistance of the line and neutral is ?? ohms can you calculate the volt drop on these conductors,
as Jstephens said he got 11.4v I think I did too
But I am sure that I forgot to put a 1.2 correction factor into the equation,
Cheers Chris.
 
you definetly have to use the x 1.2 to allow for max operating temp of 70 degrees, i did the same exam
just passed my practical today!!!
 
Last edited:

Reply to just took my 2391 test in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
389
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
971
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
There isn't anywhere to really revise on this it is down to knowledge and experience of seeing a scenario and seeing what is wrong if anything. If...
Replies
4
Views
2K
  • Question
My older card has it but my newer card doesn’t
    • Like
Replies
1
Views
772

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top