Hi,
If you're a spark, you're reading this, your name is Kevin, you work in the Manchester area and you did a job in Rusholme yesterday on lights that kept tripping the RCD - Please reconsider your career before you do serious damage.
It's forgivable that you were unable to diagnose an insulation fault with the lights and blamed it on a faulty RCD (though the customer said you thought it was both RCDs which should have made you think again). I presume you don't have the right equipment for insulation & RCD testing?
It's also forgivable taking the lights off the RCD as a tempary measure.
What isn't forgivable is taking the 1.5mm lighting circuit with an insulation fault on it, taking it off the 6A breaker and putting it directly on the main ccu switch protected only by the suppliers 100A fuse! To compound matters you didn't even put it on the consumer side. Instead putting it on the supply side so when the customer was getting a firework display last night - they couldn't even isolate the electrics!!!
I don't know how much current was going through the light fitting but even the copper had disintergrated.
I seriously believe if I hadn't attended at 1am this morning there wouldn't be a house still standing.
 
Hi,
If you're a spark, you're reading this, your name is Kevin, you work in the Manchester area and you did a job in Rusholme yesterday on lights that kept tripping the RCD - Please reconsider your career before you do serious damage.
It's forgivable that you were unable to diagnose an insulation fault with the lights and blamed it on a faulty RCD (though the customer said you thought it was both RCDs which should have made you think again). I presume you don't have the right equipment for insulation & RCD testing?
It's also forgivable taking the lights off the RCD as a tempary measure.
What isn't forgivable is taking the 1.5mm lighting circuit with an insulation fault on it, taking it off the 6A breaker and putting it directly on the main ccu switch protected only by the suppliers 100A fuse! To compound matters you didn't even put it on the consumer side. Instead putting it on the supply side so when the customer was getting a firework display last night - they couldn't even isolate the electrics!!!
I don't know how much current was going through the light fitting but even the copper had disintergrated.
I seriously believe if I hadn't attended at 1am this morning there wouldn't be a house still standing.
Somebody whos an extreme cowboy is not even fit to work as a burger flipper.
 
I tend not to call scaffolders any names, especially the ones with big calloused hands. :eek:
even the ones with soft cissy hands can drop a hammer on your head from 40ft.
 
Fortunately, I don't go near building sites these days. I do hold them in admiration mind; anyone stupid enough to shiny down a scaffold pole --- feet up without anyway of stopping, has got to be a complete nincompoop. Not that I would tell him not to.
 
Yep. Years ago H&S wasn't even a consideration, not so nowadays. Think the pendulum has now swung too far in the opposite direction.

According to the CDM 2015, I now have to complete a risk assessment when I go to Mrs Miggins house (doing a lot of work there recently?) to change her light bulbs (lamps to some). Madness I tell you, madness :eek:
 
Yep. Years ago H&S wasn't even a consideration, not so nowadays. Think the pendulum has now swung too far in the opposite direction.

According to the CDM 2015, I now have to complete a risk assessment when I go to Mrs Miggins house (doing a lot of work there recently?) to change her light bulbs (lamps to some). Madness I tell you, madness :eek:
 
Yep. Years ago H&S wasn't even a consideration, not so nowadays. Think the pendulum has now swung too far in the opposite direction.

According to the CDM 2015, I now have to complete a risk assessment when I go to Mrs Miggins house (doing a lot of work there recently?) to change her light bulbs (lamps to some). Madness I tell you, madness :eek:
my misuss eats all the CDM so i have to make do with Bournville. prefer it anyway. milk choc is sickly.
 
You idiot, Bovrnvrill is a beef extract drink, not chocolate. You've been consuming too much of that chocolate stout!
Bournville, you pillock, not bovril.:D:D:D.
[ElectriciansForums.net] Kevin please change careers before killing someone
 

Reply to Kevin please change careers before killing someone in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
388
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
971
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top